Tamper resistant outlets in detached garage #210798 08/07/13 12:10 AM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
Think I made a mistake when ordering my recpts. for a detached garage for a "dwelling". I got regular outlets, and if I'm reading right, they have to be tamper resistant. Is this right? thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Tamper resistant outlets in detached garage [Re: sparkync] #210800 08/07/13 01:26 AM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
Interesting question. I think the AHJ has some wiggle room for an interpretation there.
210.52(G) does require the receptacle in the garage but 406.12 says "In dwelling units" not a building associated with a dwelling.
I still think most would say everything needs to be TR if you don't fit an exception.
If NFPA stays true to form all of the exceptions will go away soon.


Greg Fretwell
Re: Tamper resistant outlets in detached garage [Re: sparkync] #210802 08/07/13 08:32 AM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
IMHO, I would say 'no'. However, 99%+ of the ECs have only TR devices. There reasoning is having only TR devices avoids the possibility of installation errors.

They look at the overall dollars and sense of the possibility of having a red tag due to a non-TR device being installed, and the cost of going back.

Although there is no written exception to 406.12, I would not make an issue of this.


John
Re: Tamper resistant outlets in detached garage [Re: sparkync] #210803 08/07/13 10:07 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
John brings up a good point.
I did a hospital a while back and the only receptacles that they stocked were the hospital grade even though they did a lot of work in the offices.
They told me that this actually reduced their costs because none of their electricians even had to make a return trip to the stockroom after realizing that they had picked up the wrong device.
Of course they were also concerned that a commercial grade receptacle might otherwise find its way into a patient room...but that's a whole different concern.


Ghost307
Re: Tamper resistant outlets in detached garage [Re: sparkync] #210808 08/07/13 11:37 AM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
That brings up an interesting point. Is it even legal to install a "hospital grade" marked receptacle on a circuit without the redundant ground?


Greg Fretwell
Re: Tamper resistant outlets in detached garage [Re: sparkync] #210815 08/07/13 07:53 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
1) Detached structures are not part of the dwelling. TR not required, nor is AFCI. Call it a 'loophole,' and you've got it backwards. Not too long ago, those things were the exception, not the norm

2) "Hospital grade" marking has absolutely nothing to do with what sort of wiring method is used. "Hospital Grade" simply means the device has met tighter plug retention and corrosion tests.

You want to unravel a conundrum, ask why you can't replace a "WR" device with a "hospital grade" device, when the hospital grade device meets even tougher corrosion tests than the WR one.

Re: Tamper resistant outlets in detached garage [Re: sparkync] #210818 08/07/13 11:20 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
Well whether they require it to have them or not, I think I got around it with the exception. It says if they are over 5ft. 6", they don't have to be. The owner wanted them high so he can plug in a shop light, so I put them 66 1/4" smile

Re: Tamper resistant outlets in detached garage [Re: sparkync] #210819 08/08/13 08:22 AM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
Ghost:
The medical center here in town only orders/stocks hospital grade devices for the same reasons. They have been doing that for years.

Reno:
I am under the impression that the plastic in the WR devices is supposed to be 'better', along with the internals.



John
Re: Tamper resistant outlets in detached garage [Re: gfretwell] #210821 08/08/13 12:34 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
Absolutely ok to use hospital grade receptacles wherever TR are not required. They are the highest grade of non explosion proof devices and I'd guess even explosion proof are about the enclosure.
The redundant insulated ground is about verification of voltage rise and bonding testing without adding in all the other parallel paths. It is also about reducing voltage rise between any 2 conductive points in cases of faults to ensure no current is using the patient as a parallel path.
Hospital grade receptacles don't isolate the mounting strap like Isolated ground outlets do.

Re: Tamper resistant outlets in detached garage [Re: renosteinke] #210822 08/08/13 12:40 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
I can't say I have seen a WR outlet? Does it mean Weather Resistant? Not a Canadian Requirement. I would guess that Hospital grade may be more corrosion resistant but are not subjected to the same test procedure as WR in the product standard so maybe the HG are in fact better made but no one has paid to test them to prove it? The testing system is about proving your product meets the standard and not just promising it will like they do in Europe.
Maybe the guts of WR and HG are the same and only missing the green dot?

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 3
Popular Topics(Views)
275,400 Are you busy
209,293 Re: Forum
196,586 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3