I was recently hired to make corrections to a job originally done by the home owner. The home owner has moved away and is trying to get a final inspection so that he can sell the house. I called the inspector and asked him what violations needed to be corrected. His reply blew me away because I have never herd an interpretation of the code like this one.
Here's the layout, picture this: 400 Amp, underground service, to a 320 Amp, outdoor meter pan, the meter pan has no main breakers, it's lugs out only. There are two distributions panels each one having it's own 200 Amp main circuit breaker. The wiring method between the meter pan and the two main-distribution panels is #4/0Alu SEU cable. Each SEU cable is no more then 4 feet. Everything in the panels looks code compliant, including all grounding & bonding.
Now there's the problem, the inspector is stating that because there is a swimming pool on the premises the SEU cable between the meter pan and the main-distribution panel which serves the pool must be replaced with a wiring method specified in 680.25 (A) (we are still on the 2005). He sites 680.25 as his reason.
I fully understand the restrictions and mandatory wiring methods to be used from a main panel to a sub-panel serving pool loads (feeders & branch circuits). But I do not be-leave it is the intention of 680.25 to apply these restrictions to the wiring methods prior to the main switch. It basically boils down to, do we need to have an insulated equipment grounding conductor starting at the meter or service head.
For clarification I asked the inspector the following question: so if I had a single family house with a 200 Amp overhead service wired with Aluminum SEU cable as the wiring method between the point of attachment and the meter pan, that house could not have a swimming pool, given everything is new and we are not applying any of the exceptions. His reply was "correct".
Since he's citing 680.25: 680.25 Feeders. These provisions shall apply to any feeder on the supply side of the panel-boards supplying branch circuits for pool equipment covered in Part II of this article and on the load side of the service equipment of source of a separately derived system.
He's using the part stating "AND ON THE LOAD SIDE OF THE SERVICE EQUIPMENT". Well I have to admit, it does seem like he might be on to something because the SEU is on the load side of the meter pan, but is the meter pan considered "service equipment". I can't be-leave that this was the intent of 680.25 I would appreciate any comments on this subject.
|
|
|
|
Joined: Apr 2002
Posts: 7,412 Likes: 7
Member
|
Stu: IMHO, the 'load side' of the service equipment is anything past the first means of disconnect.
This is from the '11 NEC Article 100 definitions: "Service Equipment. The necessary equipment, usually consisting of a circuit breaker(s) or switch(es) and fuse(s) and their accessories, connected to the load end of service conductors to a building or other structure, or an otherwise designated area, and intended to constitute the main control and cutoff of the supply."
Now, what is the actual scope of work that is being inspected? The pool, or the 320 service??
Would you be allowed by your POCO to have a GEC within the 320 meter pan? Here in NJ (PSE&G) that is a no-no. The GEC is at the first means of disconnect (your 200 amp panels) Is the inspector intimating that you need a 'main'?
John
|
|
|
|
Joined: Jul 2004
Posts: 10,006 Likes: 37
Member
|
Exception: An existing feeder between an existing remote panelboard and service equipment shall be permitted to run in flexible metal conduit or an approved cable assembly that includes an equipment grounding conductor within its outer sheath. The equipment grounding conductor shall comply with 250.24(A)(5).
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,412 Likes: 7
Member
|
Greg: The OP stated that the exceptions will not be used.
My question within my comments above is:
What is the inspection for?? Pool, Service?? or ??
John
|
|
|
|
Joined: Mar 2001
Posts: 27
OP
Member
|
The pool came 1st, then at some point after the pool was installed, the owner replaced the service. Just so we are clear, this whole thing has to do with the wiring method from the main-less meter pan to the main switch, beyond this is not an issue.
|
|
|
|
Joined: Mar 2001
Posts: 27
OP
Member
|
The Inspection is for the Service.
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
I was recently hired to make corrections to a job originally done by the home owner. The home owner has moved away and is trying to get a final inspection so that he can sell the house. I called the inspector and asked him what violations needed to be corrected. His reply blew me away because I have never herd an interpretation of the code like this one.
Here's the layout, picture this: 400 Amp, underground service, to a 320 Amp, outdoor meter pan, the meter pan has no main breakers, it's lugs out only. There are two distributions panels each one having it's own 200 Amp main circuit breaker. The wiring method between the meter pan and the two main-distribution panels is #4/0Alu SEU cable. Each SEU cable is no more then 4 feet. Everything in the panels looks code compliant, including all grounding & bonding.
Now there's the problem, the inspector is stating that because there is a swimming pool on the premises the SEU cable between the meter pan and the main-distribution panel which serves the pool must be replaced with a wiring method specified in 680.25 (A) (we are still on the 2005). He sites 680.25 as his reason.
I fully understand the restrictions and mandatory wiring methods to be used from a main panel to a sub-panel serving pool loads (feeders & branch circuits). But I do not be-leave it is the intention of 680.25 to apply these restrictions to the wiring methods prior to the main switch. It basically boils down to, do we need to have an insulated equipment grounding conductor starting at the meter or service head.
For clarification I asked the inspector the following question: so if I had a single family house with a 200 Amp overhead service wired with Aluminum SEU cable as the wiring method between the point of attachment and the meter pan, that house could not have a swimming pool, given everything is new and we are not applying any of the exceptions. His reply was "correct".
Since he's citing 680.25: 680.25 Feeders. These provisions shall apply to any feeder on the supply side of the panel-boards supplying branch circuits for pool equipment covered in Part II of this article and on the load side of the service equipment of source of a separately derived system.
He's using the part stating "AND ON THE LOAD SIDE OF THE SERVICE EQUIPMENT". Well I have to admit, it does seem like he might be on to something because the SEU is on the load side of the meter pan, but is the meter pan considered "service equipment". I can't be-leave that this was the intent of 680.25 I would appreciate any comments on this subject.
I disagree with the inspectors interpretation. The line and load conductors of the meter pan are service conductors. This has nothing to do with 680.25 which covers feeders.
|
|
|
|
Joined: Jul 2004
Posts: 10,006 Likes: 37
Member
|
John is right, until you get to the service disconnect, they are service conductors. Service Conductors. The conductors from the service point to the service disconnecting means. article 100 That is why you need that hardware to be marked "suitable for use as service equipment"
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,412 Likes: 7
Member
|
OK, I have to ask....what does an existing pool have to do with a service upgrade??
IMHO, It is time to respectfully speak to this inspectors superior! Hopefully, he has one.
John
|
|
|
|
Joined: May 2013
Posts: 2
New Member
|
New in New Jersey Like to know how you made out with the pool Having. kind of same problem New pool inspector says I can't use. UF Does not have cover on ground 340.108 the cable shall be permitted to have an insulated or bare grounding conductor Can't find any thing like it in 680 680.25 (A) (1) feeders does not talk about UF. Thanks Wire101
|
|
|