#210366 - 06/18/13 08:30 PM Outdoor receptacles  
twh  Offline
Member
Joined: Mar 2004
Posts: 922
Regina, Sask.
In Canada, an outside plug facing down does not need an in-use cover. Is there a similar rule in the NEC?


2017 / 2014 NEC & Related Books and Study Guides

#210368 - 06/18/13 09:34 PM Re: Outdoor receptacles [Re: twh]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,883
Brick, NJ USA
This is from the '11 NEC:

406.9 Receptacles in Damp or Wet Locations.
(A) Damp Locations. A receptacle installed outdoors in a
location protected from the weather or in other damp locations shall have an enclosure for the receptacle that is
weatherproof when the receptacle is covered (attachment
plug cap not inserted and receptacle covers closed).
An installation suitable for wet locations shall also be
considered suitable for damp locations.
A receptacle shall be considered to be in a location
protected from the weather where located under roofed
open porches, canopies, marquees, and the like, and will
not be subjected to a beating rain or water runoff. All 15-
and 20-ampere, 125- and 250-volt nonlocking receptacles
shall be a listed weather-resistant type.

Hope this helps.


John

#210370 - 06/18/13 09:56 PM Re: Outdoor receptacles [Re: twh]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,883
Brick, NJ USA
Interesting fact is the device has to be 'WR', although the wording 'in a location protected from the weather.....'

Does CEC require WR (Weather resistant) receptacles?



John

#210383 - 06/18/13 11:48 PM Re: Outdoor receptacles [Re: twh]  
twh  Offline
Member
Joined: Mar 2004
Posts: 922
Regina, Sask.
Thanks for the info.

Weather resistant receptacles aren't in the CEC. I never heard of them until now.



Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.7613 MB (Peak: 0.8936 MB) Zlib enabled. Server Time: 2017-12-17 13:49:18 UTC