nmd90 used in pvc pipe and under deck #210364
06/17/13 07:14 PM
06/17/13 07:14 PM
C
cdnrebel  Offline OP
New Member
Joined: Jun 2013
Posts: 5
canada
I know this must have been asked before but I cannot find information. Table 19 nmd90 used in dry and damp locations, note 15. What is thermoplastic jacket? I am running #6 to pony panel in a pool shed, using pvc pipe underground 30 feet, under a deck for 10 feet then into house. Any suggestions?

Tools for Electricians:
Re: nmd90 used in pvc pipe and under deck [Re: cdnrebel] #210365
06/18/13 03:44 PM
06/18/13 03:44 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
I think an underground raceway is a wet location. You can't put nmd90 in a wet location. ("d" is for dry?). Pulling a cable into a raceway is controversial. It seems you can put it in a water line but some inspectors won't allow it in pvc, because pvc is a raceway and a water line isn't.

I would probably use teck and direct bury. teck is good for anything, including rodents. The other option is nmwu.

Re: nmd90 used in pvc pipe and under deck [Re: cdnrebel] #210390
06/19/13 10:49 AM
06/19/13 10:49 AM
J
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
Thermoplastic jacket is the plastic outer casing on the cable.
AC90 has a metal jacket as opposed to the thermoplastic jacket.

Re: nmd90 used in pvc pipe and under deck [Re: cdnrebel] #210423
06/21/13 05:45 AM
06/21/13 05:45 AM
C
cdnrebel  Offline OP
New Member
Joined: Jun 2013
Posts: 5
canada
Thanks for the replies. I guess the main thing is pipe underground is wet location. I guess under a deck which the board are tight together would also be wet location. I did not get the Table 19 nmd90 note 15. All nmd90 has thermoplastic jacket on the wire, so why mention it?

Re: nmd90 used in pvc pipe and under deck [Re: cdnrebel] #210425
06/21/13 10:39 AM
06/21/13 10:39 AM
J
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
Older NM cable has paper and tar type insulation. Not sure if it was called NMD90 though. It had names like NMD7. There is probably no requirement for it to be thermoplastic and possibly someone could make it the old way.

Last edited by jdevlin; 06/21/13 10:40 AM.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
255,188 Are you busy
191,269 Re: Forum
181,026 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.004s) Memory: 0.9681 MB (Peak: 1.1094 MB) Zlib enabled. Server Time: 2019-05-24 21:05:34 UTC