Romex in break room #210018
05/22/13 09:08 AM
05/22/13 09:08 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Sorry to keep bombarding with questions, but after a long "drought"(probably spelled that wrong), work has started to come again. I have a big industrial building that has a break room built in the middle of it. It used to be an office area.It has some romex already dropped down the walls from metal junction boxes on top. Is this code compliant. Seems like it would be alright, since it is not exposed to the rest of the building. It is framed up with bathrooms on the outside perimeter of it. Don't know exactly what they will be using the building for right now, it is just an empty space they are getting ready to move into. Thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Romex in break room [Re: sparkync] #210024
05/22/13 03:48 PM
05/22/13 03:48 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,035
Brick, NJ USA
334.10 of 2008 NEC:

334.10 Uses Permitted.
Type NM, Type NMC, and Type NMS cables shall be permitted to be used in the following:
(1) One- and two-family dwellings.
(2) Multifamily dwellings permitted to be of Types III, IV, and V construction except as prohibited in 334.12.
(3) Other structures permitted to be of Types III, IV, and V construction except as prohibited in 334.12. Cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies.

There are FPNs and info on where to find the structure types within the text within the Handbook, and probably the Code book


John
Re: Romex in break room [Re: HotLine1] #210041
05/23/13 10:27 AM
05/23/13 10:27 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Thanks John.

Re: Romex in break room [Re: sparkync] #210045
05/23/13 07:18 PM
05/23/13 07:18 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
The real issue is construction type, "industrial" and "Commercial" are really meaningless in this decision.
I have seen industrial or commercial zoning in buildings that were clearly type III or even type V in some strip malls.


Greg Fretwell
Re: Romex in break room [Re: sparkync] #210050
05/23/13 10:46 PM
05/23/13 10:46 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,035
Brick, NJ USA
Greg:
I know what you mean.

When I had my EC hat on, no NM (except occasional temps) was installed in any comm jobs that I did. BX, AC, MC, and we were extatic when the aluminum jacket MC was introduced.

Industrial was EMT, RGC, IMC.



John
Re: Romex in break room [Re: sparkync] #210059
05/23/13 11:59 PM
05/23/13 11:59 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
Physical protection issues usually drive tougher wiring methods anyway but if this is in a wall romex can be OK if it is not Type I or II.


Greg Fretwell
Re: Romex in break room [Re: sparkync] #210089
05/26/13 12:48 PM
05/26/13 12:48 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
John,


Up here they use RX in com. jobs all the time as long as the building isn't type I or II. Most EC's will use #12 ga wire, but I have seen #14 wire in there too.

Re: Romex in break room [Re: sparkync] #210093
05/26/13 03:28 PM
05/26/13 03:28 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Somebody was napping when they changed the rules - perhaps a decade ago.

Romex was developed for, and marketed to, the residential market. I witnessed many strident representations by NM manufacturers to UL (and the code committees) that NM was only intended for use in small, simple residential buildings with wood frames.

This is why, for decades, the NEC limited the use of NM to wood-framed residential buildings of three floors or less. Three floors is as tall as you can go with wood framing; taller buildings require different construction methods.

I can't recall exactly when the NEC was re-written (99? 02?), but the NEC eliminated the earlier language completely, and instead referred to the construction type. As the code is now written, you could wire the Sears Tower, the Pentagon, and the mall of America using Romex.

Putting this in context, this was also (coincidence?) the same time the AFCI came on the market. We've seen other restrictions placed on places where Romex is likely to be used; witness the restrictions placed on residential multi-wire circuits in the 2011 edition. Romex has also been effectively banned from crawl spaces since 2008 (damp locations).

Yet, there are still plenty of localities where the use of NM (as well as "Smurf tube") is banned from anything that's not a small home. Even PVC conduit is banned in many places, except for very specialized applications (Chicago comes to mind).

Re: Romex in break room [Re: sparkync] #210096
05/27/13 03:22 AM
05/27/13 03:22 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
Quote
witness the restrictions placed on residential multi-wire circuits in the 2011 edition.


What was that change?


Greg Fretwell
Re: Romex in break room [Re: sparkync] #210098
05/27/13 01:49 PM
05/27/13 01:49 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
What are the specifications for Type 1 and 2 walls. I can't seem to see a clear definition of it by searching the web.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,352 Are you busy
187,976 Re: Forum
177,520 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 16 (0.004s) Memory: 1.0273 MB (Peak: 1.2064 MB) Zlib enabled. Server Time: 2018-10-17 23:42:13 UTC