3 phase feeder with only (1) 120 volt circuit #209951 05/17/13 11:32 AM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
I have a feeder feeding several Refrigerant motors. The total amperage after applying the 125% for the largest motor comes out to 93.42 amps counting 1 small cooler evaporator that is 120 volts that only pulls 4.73 amps. Is there any reduction of the neutral in a case like this or is it just applied over 200 amps? The rest of the load has no neutral. Thanks..

2017 / 2014 NEC & Related Books and Study Guides
Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209952 05/17/13 12:10 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
Also I have a 3 phase feeder. It's been a long time since I've figured up a 3 phase feeder. Do I divide the total amps by 3?? 93.42 (94 amps)/3= 31.33 ??

Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209953 05/17/13 04:51 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Originally Posted by sparkync
Also I have a 3 phase feeder. It's been a long time since I've figured up a 3 phase feeder. Do I divide the total amps by 3?? 93.42 (94 amps)/3= 31.33 ??


Are they single phase motors spread equally across the phases, or are they 3-phase motors?

Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209954 05/17/13 04:55 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
No, there are (3) 3 phase motors, (4) 208/240 volt single phase motors, and (1) 120 volt single phase motor

Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209958 05/17/13 09:50 PM
Joined: Jul 2004
Posts: 9,557
G
gfretwell Offline
Member
I read 220.61 as saying you could use a #14 for a neutral if your max neutral load is 4 or 5 amps.



Greg Fretwell
Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209960 05/18/13 11:33 AM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
Greg, if you don't mind me asking, how do you come up with this? thanks. I'm reading from 2011 Code.

Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209961 05/18/13 12:49 PM
Joined: Jul 2004
Posts: 9,557
G
gfretwell Offline
Member
Quote
220.61 Feeder or Service Neutral Load.
(A) Basic Calculation. The feeder or service neutral load
shall be the maximum unbalance of the load determined by
this article. The maximum unbalanced load shall be the
maximum net calculated load between the neutral conductor
and any one ungrounded conductor.
Exception: For 3-wire, 2-phase or 5-wire, 2-phase systems,
the maximum unbalanced load shall be the maximum
net calculated load between the neutral conductor and any
one ungrounded conductor multiplied by 140 percent


I do not see anything that would make you use more than a #14 if the only unbalanced load is a 4 amp single phase motor.

In the computer room biz we never even brought a neutral beyond the service disconnect because there was never any unbalanced load. (everything was line to line)


Greg Fretwell
Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209962 05/18/13 04:34 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
Thanks Greg. I just wanted to make sure there was not another rule I was missing in the code. I'll figure a bigger neutral just in case in the future they want to add something else that is 120 volts. In fact there is an old outlet attached to one of the units, that the owner said they wouldn't need, but now that I think about it, an outlet is required for "service means" on a roof top. Thanks again

Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209963 05/18/13 05:53 PM
Joined: Jul 2004
Posts: 9,557
G
gfretwell Offline
Member
If you serve that outlet from another phase, you are still OK with a #14 if it is a 15a circuit. (the way I read it)

I agree as a design issue, running a bigger neutral is probably a good idea.


Greg Fretwell
Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209983 05/20/13 12:24 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
Article 215
215.2 (A) 2
Grounded Conductor.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 74
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 18
NORCAL 12
Popular Topics(Views)
274,137 Are you busy
207,943 Re: Forum
195,594 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3