3 phase feeder with only (1) 120 volt circuit #209951
05/17/13 11:32 AM
05/17/13 11:32 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
I have a feeder feeding several Refrigerant motors. The total amperage after applying the 125% for the largest motor comes out to 93.42 amps counting 1 small cooler evaporator that is 120 volts that only pulls 4.73 amps. Is there any reduction of the neutral in a case like this or is it just applied over 200 amps? The rest of the load has no neutral. Thanks..

2017 / 2014 NEC & Related Books and Study Guides
Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209952
05/17/13 12:10 PM
05/17/13 12:10 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Also I have a 3 phase feeder. It's been a long time since I've figured up a 3 phase feeder. Do I divide the total amps by 3?? 93.42 (94 amps)/3= 31.33 ??

Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209953
05/17/13 04:51 PM
05/17/13 04:51 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Originally Posted by sparkync
Also I have a 3 phase feeder. It's been a long time since I've figured up a 3 phase feeder. Do I divide the total amps by 3?? 93.42 (94 amps)/3= 31.33 ??


Are they single phase motors spread equally across the phases, or are they 3-phase motors?

Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209954
05/17/13 04:55 PM
05/17/13 04:55 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
No, there are (3) 3 phase motors, (4) 208/240 volt single phase motors, and (1) 120 volt single phase motor

Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209958
05/17/13 09:50 PM
05/17/13 09:50 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
I read 220.61 as saying you could use a #14 for a neutral if your max neutral load is 4 or 5 amps.



Greg Fretwell
Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209960
05/18/13 11:33 AM
05/18/13 11:33 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Greg, if you don't mind me asking, how do you come up with this? thanks. I'm reading from 2011 Code.

Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209961
05/18/13 12:49 PM
05/18/13 12:49 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
Quote
220.61 Feeder or Service Neutral Load.
(A) Basic Calculation. The feeder or service neutral load
shall be the maximum unbalance of the load determined by
this article. The maximum unbalanced load shall be the
maximum net calculated load between the neutral conductor
and any one ungrounded conductor.
Exception: For 3-wire, 2-phase or 5-wire, 2-phase systems,
the maximum unbalanced load shall be the maximum
net calculated load between the neutral conductor and any
one ungrounded conductor multiplied by 140 percent


I do not see anything that would make you use more than a #14 if the only unbalanced load is a 4 amp single phase motor.

In the computer room biz we never even brought a neutral beyond the service disconnect because there was never any unbalanced load. (everything was line to line)


Greg Fretwell
Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209962
05/18/13 04:34 PM
05/18/13 04:34 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Thanks Greg. I just wanted to make sure there was not another rule I was missing in the code. I'll figure a bigger neutral just in case in the future they want to add something else that is 120 volts. In fact there is an old outlet attached to one of the units, that the owner said they wouldn't need, but now that I think about it, an outlet is required for "service means" on a roof top. Thanks again

Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209963
05/18/13 05:53 PM
05/18/13 05:53 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
If you serve that outlet from another phase, you are still OK with a #14 if it is a 15a circuit. (the way I read it)

I agree as a design issue, running a bigger neutral is probably a good idea.


Greg Fretwell
Re: 3 phase feeder with only (1) 120 volt circuit [Re: sparkync] #209983
05/20/13 12:24 PM
05/20/13 12:24 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
Article 215
215.2 (A) 2
Grounded Conductor.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 222
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,138 Are you busy
189,144 Re: Forum
178,815 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 16 (0.004s) Memory: 1.0257 MB (Peak: 1.2081 MB) Zlib enabled. Server Time: 2018-12-11 02:52:48 UTC