Underground Risers #209941 05/16/13 01:42 PM
Joined: Jun 2012
Posts: 74
akmaster Offline OP
Member
Is there any code section requiring risers and the 90 from a duct bank to be schedule 80 PVC or Rigid Conduit? I think it comes down to physical damage but on the job we have a 13.8 duct bank of schedule 40 pvc that has pvc 90's and risers that I feel need to be and the SPECS call for galvanized rigid conduit..

any help on what NEC says would be appreciated...see pic attached.

Thank you,

Greg

Attached Files underground.JPG

Don't drive and TEXT! Drive now TALK LATER!
2017 / 2014 NEC & Related Books and Study Guides
Re: Underground Risers [Re: akmaster] #209942 05/16/13 02:38 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Online Content
Member
300.5(D)(4) is what you are talking about.

Quote

(D) Protection from Damage. Direct-buried conductors and cables shall be protected from damage in accordance with 300.5(D)(1) through (D)(4).

(4) Enclosure or Raceway Damage. Where the enclosure or raceway is subject to physical damage, the conductors shall be installed in rigid metal conduit, intermediate metal conduit, Schedule 80 PVC conduit, or equivalent.


It still brings up that ambiguous "subject to physical damage" thing.



Greg Fretwell
Re: Underground Risers [Re: akmaster] #209943 05/16/13 02:52 PM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
The 'over 600 volts' (300-31 to 300-50) basically is what Greg said above.

That said, who wrote the 'Specs' you referenced above??

'Specs' should be followed, or a letter from the writer (assume an engineer) allowing a change should be obtained.



John
Re: Underground Risers [Re: akmaster] #209944 05/16/13 02:53 PM
Joined: Jun 2012
Posts: 74
akmaster Offline OP
Member
Thank you Greg!

regards

Greg


Don't drive and TEXT! Drive now TALK LATER!
Re: Underground Risers [Re: akmaster] #209945 05/16/13 04:14 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Online Content
Member
I used to see a lot of RNC sweeps on these risers because pulling wires around those corners can actually cut into PVC.
Around the water, they can still rust out so it is going to be a compromise around here.


Greg Fretwell
Re: Underground Risers [Re: akmaster] #209984 05/20/13 12:48 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
We always Put RSC 90's As gfretwell said. for the same reason. Lots of times the nylon pull string or the pulling rope would pull thru the 90's. If the RSC 90 extends above ground it should be bonded. Utility companys as well as others use PVC u guard & sch. 80 up the pole.
Just my 2 cents worth


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,544 Are you busy
209,453 Re: Forum
196,847 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3