Hi,
I have a situation where about 15 indoor transformers are being used outdoors without the proper hood to make them Nema 3R. Could anyone point me to the CFR 1926 reg or the NEC code regarding this violation?


These transformers are being used for temp power..

Thank you

Greg

Last edited by akmaster; 05/07/13 04:48 PM.

Don't drive and TEXT! Drive now TALK LATER!
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
110.11 Deteriorating Agents.
Unless identified for use in the operating environment, no conductors or equipment shall be located in damp or wet locations; where exposed to gases, fumes, vapors, liquids, or other agents that have a deteriorating effect on the conductors or equipment; or where exposed to excessive temperatures.
FPN No. 1: See 300.6 for protection against corrosion.
FPN No. 2: Some cleaning and lubricating compounds can cause severe deterioration of many plastic materials used for insulating and structural applications in equipment.
Equipment not identified for outdoor use and equipment identified only for indoor use, such as “dry locations,” “indoor use only,” “damp locations,” or enclosure Types 1, 2, 5, 12, 12K, and/or 13, shall be protected against permanent damage from the weather during building construction.