NEC 1993-Pool and service wires overhead question #209847
05/07/13 01:28 PM
05/07/13 01:28 PM
HappyElectrician  Offline OP
Member
Joined: Dec 2011
Posts: 31
Penn USA
Does anyone have a copy of the 1993 NEC to see what it stated as to how far away overhead service wires must be from the parimiter of a pool.

It would be greatly appreciated
Thank you

2017 / 2014 NEC & Related Books and Study Guides
Re: NEC 1993-Pool and service wires overhead question [Re: HappyElectrician] #209848
05/07/13 01:54 PM
05/07/13 01:54 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,182
Estero,Fl,usa
The picture is the same as 680.8 but the clearances are shorter

_______________________________________________________________________
A. Clearance in any
direction to the
water level, edge
of water surface,
base of diving
platform, or
permanently-anchored raft

Insulated Cables, 0750 Volts to Ground, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor

18 ft

All other conductors
0-15kv
25 ft

>15kv
27 ft

_______________________________________________________________________
B. Clearance in any
direction to the
diving platform or tower

Insulated Cables, 0750 Volts to Ground, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor
14 ft

All other conductors
0-15kv

16 ft

>15kv

18 ft

_______________________________________________________________________
C. Horizontal limit
of clearance
measured from This limit shall extend to the outer edge
inside wall of the of the structures listed in (1) and (2)
pool above but not less than 10 ft.
_______________________________________________________________________

Copyright 1992, NFPA



Greg Fretwell
Re: NEC 1993-Pool and service wires overhead question [Re: gfretwell] #209897
05/10/13 01:54 PM
05/10/13 01:54 PM
HappyElectrician  Offline OP
Member
Joined: Dec 2011
Posts: 31
Penn USA
Thanks so much for your reply. Much appreciated.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 222
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,084 Are you busy
181,127 Re: Forum
171,323 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.9521 MB (Peak: 1.0775 MB) Zlib enabled. Server Time: 2018-02-25 15:48:57 UTC