ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Al Hildenbrand - Minneapolis - obituary
by Bill Addiss - 02/03/23 07:38 PM
Violation?
by renosteinke - 01/27/23 09:52 PM
Does NEC 551.71 (F) apply to dwellings?
by BigB - 01/20/23 10:46 AM
Power submeter connections
by HotLine1 - 01/19/23 09:09 AM
New in the Gallery:
Burger King crown sillyness
Burger King crown sillyness
by wa2ise, December 11
240/208 to a house
240/208 to a house
by wa2ise, October 9
Who's Online Now
0 members (), 129 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#209273 03/20/13 10:17 PM
Joined: Mar 2005
Posts: 240
Member
I know NEC will allow EMT in concrete with proper corrosion protection, I have always used pvc from day one on the job.
What do you use to install it in the concrete?

I only ask because the SUPER-Foreman on the job I am working at, scoffed at me when I questioned his decision to run emt from parking garage though pan deck up to next level, which they poured the concrete today.

However as I have said before I am in WA state, and we have a state code which supersedes NEC WAC 296-46B-358 which strictly forbids this type of installation not to mention there was no type of corrosion protection talked about in 300.6 just straight EMT(3. I tried to explain that I didn't think this was a good idea...unfortunately as I said he believes he is "Super E"

Thanks,
H20

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Jul 2004
Posts: 9,788
Likes: 14
G
Member
RNC or RMC is about all I see in concrete unless they go with smurf. Metal seems to fail right at the top of the pour where it comes out. There are 2 schools of thought. Some say it is a chemical thing where the metal reacts with the concrete where they come together in air. The other thought is simpler. They assume that is just where water pools.


Greg Fretwell
Joined: Jun 2004
Posts: 1,273
T
Member
Out in my area, local, specific, rules prohibit the practice.

Once saw a guy red tagged over it.

He was using the NEC -- and never slowed down to read the local regs.

!


Tesla
Joined: Feb 2002
Posts: 2,233
H
Member
Greg,

I believe the stuff they call "Mambo" cable is also listed for concrete. It looks metal greenfield with wire in it and it is coated with plastic. It is listed for underground too and I also believe pool wiring.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Top Posters(30 Days)
triple 3
BigB 3
Popular Topics(Views)
303,136 Are you busy
232,161 Re: Forum
216,887 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5