EMT in concrete #209273 03/20/13 11:17 PM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
I know NEC will allow EMT in concrete with proper corrosion protection, I have always used pvc from day one on the job.
What do you use to install it in the concrete?

I only ask because the SUPER-Foreman on the job I am working at, scoffed at me when I questioned his decision to run emt from parking garage though pan deck up to next level, which they poured the concrete today.

However as I have said before I am in WA state, and we have a state code which supersedes NEC WAC 296-46B-358 which strictly forbids this type of installation not to mention there was no type of corrosion protection talked about in 300.6 just straight EMT(3. I tried to explain that I didn't think this was a good idea...unfortunately as I said he believes he is "Super E"

Thanks,
H20

2017 / 2014 NEC & Related Books and Study Guides
Re: EMT in concrete [Re: watersparkfalls] #209277 03/20/13 11:36 PM
Joined: Jul 2004
Posts: 9,608
G
gfretwell Online Content
Member
RNC or RMC is about all I see in concrete unless they go with smurf. Metal seems to fail right at the top of the pour where it comes out. There are 2 schools of thought. Some say it is a chemical thing where the metal reacts with the concrete where they come together in air. The other thought is simpler. They assume that is just where water pools.


Greg Fretwell
Re: EMT in concrete [Re: watersparkfalls] #209280 03/21/13 05:49 AM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
Out in my area, local, specific, rules prohibit the practice.

Once saw a guy red tagged over it.

He was using the NEC -- and never slowed down to read the local regs.

!


Tesla
Re: EMT in concrete [Re: watersparkfalls] #209305 03/23/13 11:58 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
Greg,

I believe the stuff they call "Mambo" cable is also listed for concrete. It looks metal greenfield with wire in it and it is coated with plastic. It is listed for underground too and I also believe pool wiring.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 19
Admin 8
Popular Topics(Views)
278,810 Are you busy
211,973 Re: Forum
199,011 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3