#209233 03/17/13 04:05 PM
Joined: Mar 2004
Posts: 785
B
BigB Offline OP
Member
Two metal halide fixtures were accidentally re-lamped with HPS lamps. We were going to switch them back to MH lamps, problem is the HPS lamps are working fine and the HOA wants them in all the fixtures now. I don't even know how they are working with no igniter, but they are working. Not sure how long though, it's only been 3 weeks. Anyone know why they are working and if they will hold up?

Maybe the fixtures were originally HPS and were lamped with MH?

Joined: May 2003
Posts: 1,157
Member

Joined: Mar 2004
Posts: 785
B
BigB Offline OP
Member
nope, just plain old HPS lamps

Joined: Oct 2000
Posts: 2,722
Broom Pusher and
Member
There are many varieties of Pulse-Start Metal Halide Fixtures available for Lamp Wattage of 35 Watts up to 400 Watts.

AFAIK, the PSMH Ballast Kits use the same Pulse Ignitors as HPS Ballast Kits - per Lamp Wattage.

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Mar 2013
Posts: 46
Member
Originally Posted by BigB
I don't even know how they are working with no igniter, but they are working.
Maybe the fixtures were originally HPS and were lamped with MH?


Probe-start MH ballasts do not have ignitors, but they are an older (though still current) tech. Pulse-start (new tech) ballasts DO have ignitors.

As to what the fixtures are actually supposed to be, check the transformer for the ANSI code... prefix M for MH, S for HPS. It's typically a letter and two numbers, like M47 or S55.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Top Posters(30 Days)
LarryC 3
NORCAL 2
Popular Topics(Views)
291,341 Are you busy
223,834 Re: Forum
209,232 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5