Receptacle in Dining room #209020 03/03/13 07:33 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline OP
Member
Okay, so here's my next question: Can a switched receptacle be on a small appliance branch circuit for dining room lighting?


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Receptacle in Dining room [Re: George Little] #209021 03/03/13 08:14 PM
Joined: Jun 2004
Posts: 610
S
shortcircuit Offline
Member
IMO...no. 210.52(B)(2) says no other outlets can be on the small appliance branch circuits

Re: Receptacle in Dining room [Re: George Little] #209027 03/03/13 11:15 PM
Joined: Jul 2004
Posts: 9,389
G
gfretwell Offline
Member
Interesting question.

You need to have a luminaire, switched as your required lighting outlet to satisfy 210.70)A)(1)ex1 so who is to say that it is a lighting outlet if it was on one of two SA circuits?
210.52 tends to be contradictory. On the one hand they want 2 dedicated 20s serving the counter top, then they say you can pick up just about every other receptacle in the kitchen, dining room, pantry etc on those circuits.
The handbook does show a switched lighting outlet (receptacle) on a 15a general lighting circuit.


Greg Fretwell
Re: Receptacle in Dining room [Re: George Little] #209030 03/04/13 10:18 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
Greg,

When I was in business, I would run about 3 different circuits to the kitchen. On one circuit, I would pick up 2-3 recpt. in kitchen and some in dining room. On another circuit, I would pick up 2-3 recpt. in kitchen then pick up some breakfast nook recpt. The last kitchen circuit would stay in the kitchen and they would have 3-4 recpt on it. Depending on the size of the kitchen.

Re: Receptacle in Dining room [Re: George Little] #209036 03/04/13 11:00 AM
Joined: Jul 2004
Posts: 9,389
G
gfretwell Offline
Member
I have seen some scary expensive houses that only had 2 for all of the required rooms. (kitchen, dining and a nook)

They also picked up 3 baths (counters) on one 20.

I was amazed at where some builders will save a buck.


Greg Fretwell
Re: Receptacle in Dining room [Re: George Little] #209040 03/04/13 03:04 PM
Joined: Apr 2002
Posts: 7,109
HotLine1 Offline
Member
I have to agree with Shortcircuit & say 'No', IF that circuit is one of the two required.

If it is an 'additional' 20 amp circuit then I feel it would be OK.

As to the bath receptacles all being on one circuit, compliant but a terrible design, and could be a major inconvenience for the occupants.


John
Re: Receptacle in Dining room [Re: George Little] #209044 03/04/13 05:19 PM
Joined: Jul 2004
Posts: 9,389
G
gfretwell Offline
Member
I wonder if George's question comes down to whether a small appliance receptacle outlet can be switched? You already have the required lighting outlet.


Greg Fretwell
Re: Receptacle in Dining room [Re: George Little] #209045 03/04/13 08:39 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline OP
Member
I'm going to go with Greg, Short Circuit and Hot line's answers. One can not switch a receptacle on a 20a. SAC to satisfy the lighting outlet requirement mentioned in 210.70. It might be a stretch because the dining room is not mentioned in the exception but the wording in 210.52(B)(2) is pretty clear "No Other Outlets" meaning no lighting outlets. IMHO.


George Little
Re: Receptacle in Dining room [Re: George Little] #209079 03/06/13 10:40 AM
Joined: Apr 2002
Posts: 7,109
HotLine1 Offline
Member
George:
IF someone wanted 1/2 of a DR outlet switched for convenience, as in controling whatever was plugged into the 1/2, that would be compliant. (Using a 20 amp listed switch)

What say you?? Opinions appreciated.


John
Re: Receptacle in Dining room [Re: George Little] #209081 03/06/13 10:45 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
John,

I think I would have to pass that type of install if I saw it.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 11
Popular Topics(Views)
258,501 Are you busy
194,117 Re: Forum
183,619 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3