ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Do You Travel?
by gfretwell - 05/10/21 06:42 PM
Any Woodworkers here?
by gfretwell - 05/10/21 06:26 PM
Your favourite food?
by gfretwell - 05/10/21 06:13 PM
Lock-down Thread
by gfretwell - 05/10/21 06:12 PM
Just be aware of this...
by Trumpy - 05/10/21 06:47 AM
New in the Gallery:
2020 - 2021 Winter Project
Garden 2021
Who's Online Now
1 registered members (gfretwell), 18 guests, and 20 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Alarm wiring and power in same J-box. #208941 02/23/13 04:09 AM
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
Hey guys thanks for the help on these little issues I
run into. I want to use NEC 300.3 (C)(1)
"Conductors of ac and dc circuits rated 600 volts ,nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. all conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable or raceway."

The voltage is 120/240 a.c. and I want to install the start and alarm conductors in the same J-box box as the power. The alarm cable specified is rated for 300 v. dc.
300.3 (C)(1) only refers to the voltage rating so I'm thinking it's OK even though the alarm conductors are only rated for dc. Right?

2017 / 2014 NEC & Related Books and Study Guides
Re: Alarm wiring and power in same J-box. [Re: wewire2] #209413 03/26/13 11:18 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
Read Informational Note #1 .

Re: Alarm wiring and power in same J-box. [Re: wewire2] #209415 03/27/13 02:03 AM
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
Thanks Yoop. I did see that but the fact that the cable met the voltage requirement but was only rated for DC is what was throwing me off. I usually separate everything but when the GC stubbs the conduits out of the concrete wrong I end up having to make things work. I don't encounter much low voltage and Article 725 still confuses me. One of the things I don't understand is how to accurately classify the circuits when you don't know what the attributes of the power source are in the equipment that is powering them. Is there an easy way to determine that or is it involved?

Last edited by wewire2; 03/27/13 02:05 AM.
Re: Alarm wiring and power in same J-box. [Re: wewire2] #209418 03/27/13 11:37 AM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
What kind of alarm?


"Live Awesome!" - Kevin Carosa
Re: Alarm wiring and power in same J-box. [Re: wewire2] #209419 03/27/13 05:37 PM
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
For this installation it was generator failure alarms.

Re: Alarm wiring and power in same J-box. [Re: wewire2] #209422 03/28/13 08:27 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
725 breaks down each. Class 1/2/ & 3. Take a look.

Re: Alarm wiring and power in same J-box. [Re: wewire2] #209431 03/29/13 02:05 PM
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
Haha! Got it! I knew I somehow must be missing a step. Totally makes sense now.

Re: Alarm wiring and power in same J-box. [Re: wewire2] #209434 03/29/13 06:15 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
Sometimes, that all it takes. Better to talk it out now then have something to smoke out later and get clarity later...


"Live Awesome!" - Kevin Carosa

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 19
Admin 8
Popular Topics(Views)
278,811 Are you busy
211,973 Re: Forum
199,011 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3