Re: transfer switch #20879 01/25/03 02:50 PM
Joined: Jun 2001
Posts: 196
C
Cindy Offline OP
Member
thank you for your thoughts on this, i'll be looking at the calcs and job site this next week.

but from the 1-line it looks wrong that the 800a s-board that was fed with 8-350's is now going to be fed from a 225a main breaker
for the whole system and 4/0 coppers to feed 3 panels rated 300a, 300a, and 200a. how can the designer do that? [not to mention the size issue of landing them/don's question]

Work Gear for Electricians and the Trades
Re: transfer switch #20880 01/25/03 11:32 PM
Joined: Jun 2001
Posts: 642
N
nesparky Offline
Member
I would look very closely at the load calcs. Also check with the poco and see what the historical load/month has been. This may have been over built for a future expansion that did not occur. I suspect that those areas will most likely have the answers-if the designer did not screw up his/her load calcs.
Sometimes owners want to do things as cheaply as possible an try to hard to save money. If designers cannot or will not tell- them sorry that will not work- you get drawings that are questionable.
Good luck on this job

[This message has been edited by nesparky (edited 01-25-2003).]


ed
Re: transfer switch #20881 01/25/03 11:53 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
It is a code violation to have a 225A main serving a 300A distribution breaker, since they can never be coordinated.


Ron
Re: transfer switch #20882 01/26/03 01:36 PM
Joined: Jun 2001
Posts: 196
C
Cindy Offline OP
Member
>>>It is a code violation to have a 225A main serving a 300A distribution breaker, since they can never be coordinated.<<<

i know i'm going to sound stupid, but where does it say that? 240.12 tlaks about coordination for orderly shutdown, 110.10 says to cordinate to rpotect equipment. but i dont see why a smaller ocpd cant protect larger ocpd's or equipment. inconvenient to the user, but is it a violation? thanks

Re: transfer switch #20883 01/26/03 01:47 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Ron
What code section requires OCPD coordination for general occupancies?
Don


Don(resqcapt19)
Page 2 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 11
Popular Topics(Views)
277,764 Are you busy
211,323 Re: Forum
198,362 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3