1 members (ale348),
302
guests, and
14
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
http://www.cooperindustries.com/con...ntal/pv-fuses/solar-pv-fuse-14x51mm.htmlBussman shows 10,000 Amps as the interrupting rating. Never forget: PV cells saturate current flow with a bolted short at much lower levels than rotary induction devices. 15, 20, 25 & 32A Notably, these fuses are designed towards the European standard; hence the 32A type.
Tesla
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
I have a little question. Has anything in the box actually ignited? Sure it looks pretty black in there, but I'm wondering if that isn't because of transmitted smoke/heat that may have come in through one of the conduits.
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
OP
Member
|
Trumpy: I have no details/info that is 'firm'.
It appeared that there was some damage in one combiner box that was not soot/heat, but meltdown. An adjacent box looked like transmitted heat/smoke/soot. Keep in mind I am not the forensic party that is looking into this.
Most of the damaged area has been removed, grid identified, boxed up & transported to an interior location to be investigated. Could ba a long haul for an answer.
John
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
OP
Member
|
Tesla:
Littlefuse KLKD-15 on another jobsite is 100K AIC for AC and 50K AIC for DC at 600 volts.
I have not been back to the problem site yet, but probably by middle of next week.
John
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
OP
Member
|
John
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
OP
Member
|
I'm getting the gut feeling that either it's going to be a long time, or kept hush-hush as to a cause.
Can't share what I don't know.
John
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
OP
Member
|
Just a bump & update.
This array is now replaced and requested a inspection be scheduled.
No cause has been mentioned to me as of today, although there have been a lot of comments.
Coincidently, there was a large fire in an adjacent Twp yesterday (Mon), ao a large whse bldg, that also has a solar panel install. The cause is not determined, either a roof fire that ignited the panels, or a panel fire that ignited the roof.
The fire chief of that Twp only heard of the fire in this thread about an hour after his fire.
John
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
Thanks for the follow up Hotline. Any determination of cause should be shared with the industry for all to learn I would hope. I know NJ had a solar boom for awhile there and I would think that some installations were not done properly. We have a solar boom here in Mass now.
|
|
|
Posts: 28
Joined: February 2011
|
|
|
|