Grounded outlets? #207894
12/06/12 11:27 PM
12/06/12 11:27 PM
S
schenimann  Offline OP
Member
Joined: Feb 2008
Posts: 193
Western North Carolina
I came across some new outlets that I had never seen before. They were in an older home that had no ground wires. They were three prongs with an orange backlight in them. There was a jumper from the ground screw to the neutral screw. Apparently whoever had done the upgrades had put a small green sticker to indicate which outlets were now "grounded". I think they were labled "Bryant". Anyone ever seen these?

Work Gear for Electricians and the Trades
Re: Grounded outlets? [Re: schenimann] #207895
12/06/12 11:32 PM
12/06/12 11:32 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,035
Brick, NJ USA
The 'small green' sticker possibly the Hospital Grade mark??



John
Re: Grounded outlets? [Re: schenimann] #207900
12/07/12 01:09 AM
12/07/12 01:09 AM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Did you happen to get a picture of it?

Re: Grounded outlets? [Re: schenimann] #207901
12/07/12 01:16 AM
12/07/12 01:16 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,274
Fullerton, CA USA
Is it like this?

http://images.drillspot.com/pimages/320/32035_300.jpg

.....an isolated ground receptacle

Re: Grounded outlets? [Re: schenimann] #207903
12/07/12 01:31 AM
12/07/12 01:31 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,035
Brick, NJ USA
The 'orange backlight' sounds interesting.

Electure has the HG/IG without the 'backlight'


John
Re: Grounded outlets? [Re: schenimann] #207904
12/07/12 02:00 AM
12/07/12 02:00 AM
M
mbhydro  Offline
Member
Joined: Feb 2003
Posts: 350
Winnipeg MB Canada
Here is one that is backlit by Byrant that I found in Google.

http://www.globalindustrial.com/p/e...vices/style-dup-rcpt-hg-15a-125v-5-15rwh

Google search turned up a few manufactures that make an illuminated hospital grade receptacle.

Until this posting I had never heard of such a thing. Never seen them in any of the hospitals here in Manitoba when I have been a patient or visitor.




Re: Grounded outlets? [Re: schenimann] #207905
12/07/12 05:13 AM
12/07/12 05:13 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
Grounding to the neutral screw is a death trap. The old 3 lite tester will certainly say they are OK, even if you have an upstream white/black reversal and the case of any grounded equipment is now 120v above ground.

I think we are dazzled by a fancy device and overlooking the violation.


Greg Fretwell
Re: Grounded outlets? [Re: schenimann] #207921
12/07/12 11:05 PM
12/07/12 11:05 PM
T
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,430
Vienna, Austria
That's been standard practice in many German regions for decades and most Eastern European countries did the same. Most Western European countries outlawed the practice some time in the 1970s, but there are still many existing installations.

Not only a black/white reversal is dangerous, a broken neutral is just as bad if anything is plugged into that outlet!

Re: Grounded outlets? [Re: schenimann] #207926
12/09/12 06:07 AM
12/09/12 06:07 AM
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,431
Bakersfield, CA (Originally Or...
I bought a 10 pack of the lighted Hubbell HG 5-15 recepts for novelty sake (and the counter guy at CED cut the price in half as they'd been on the shelf through about 5 inventory cycles..) I put one in my ex wife's sisters bathroom (GFI upstream.) She stared at it for about 10 minutes as if I'd installed something from another planet next to her med cabinet laugh

The neutral to ground jumper is a no-no if you're not a fan of getting lit up if an upstream neutral comes loose

Re: Grounded outlets? [Re: schenimann] #207931
12/09/12 12:32 PM
12/09/12 12:32 PM
M
mbhydro  Offline
Member
Joined: Feb 2003
Posts: 350
Winnipeg MB Canada
How much light do they give off? Could one be put in the bathroom (GFI protected of course) instead of a nightlight?

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,350 Are you busy
187,974 Re: Forum
177,520 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 16 (0.004s) Memory: 1.0260 MB (Peak: 1.2088 MB) Zlib enabled. Server Time: 2018-10-17 22:40:46 UTC