suspended ceiling #207627 11/12/12 05:51 PM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline OP
Member
I am back on line,and I already have a question. Any restrictions about putting a receptacle above a suspended ceiling? Is it allowed or not?

2017 / 2014 NEC & Related Books and Study Guides
Re: suspended ceiling [Re: harold endean] #207628 11/12/12 06:27 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
No problem putting in a receptacle above the dropped ceiling. These receptacles can be used for servicing equipment located above the ceiling. You cannot, however, plug in a flexible cord for a piece of equipment that is located above the ceiling and leave it plugged in. A wireless router would be an example.


Few things are harder to put up with than the annoyance of a good example.
Re: suspended ceiling [Re: harold endean] #207674 11/19/12 09:10 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline OP
Member
So a receptacle is OK just don't leave anything plugged into it.

Re: suspended ceiling [Re: harold endean] #207677 11/19/12 03:20 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
Pretty much...I always have problems with the HVAC folks who want to put a plug-in condensate pump above the ceiling tiles and whine that it should be okay because "it's just a tiny little load". I usually tell them that the only guarantee that comes with that statement is that it will "only start a tiny little fire".


Ghost307
Re: suspended ceiling [Re: harold endean] #207679 11/19/12 07:46 PM
Joined: Jul 2004
Posts: 9,439
G
gfretwell Offline
Member
How do you let them put that pump up there?



Greg Fretwell
Re: suspended ceiling [Re: harold endean] #207680 11/19/12 08:03 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Fire load, smoke load .... Humbug!

IMO, the HVAC condensate pump is a perfect example of where the NEC is simply wrong. Call it extremist, draconian, or misguided.

I disagree with the entire assumption that there can NEVER be a legitimate use of a cord above a suspended ceiling.

Oh, just hard-wire. Yea, right ... even if it were possible to replace the cordset with an MC whip, there'd be howls about 'voiding the listing.'

The HVAC needs a condensate pump. The HVAC is above the ceiling. Is this a back-door attempt to move ban the HVAC from the ceiling void?

An aside ...

Now that Ideal has a funky screwdriver for use on those multi-head screws we see so often, I fully expect some code genius to insist that you can ONLY use the funky driver on the funky heads.

That's where you wind up when you micro-manage.

Re: suspended ceiling [Re: harold endean] #207689 11/20/12 01:03 AM
Joined: Feb 2004
Posts: 1,432
Lostazhell Offline
Member
I've seen a couple places where the FAU/condensate pump was placed above the electrical room which was hard lid (and the only thing hard lid), thus not above the suspended ceiling.

I know the receptacle itself is not a code violation in itself, but I've always been reluctant to install one above T-bar mostly because I know SOMEONE (alarm guy, HVAC, tenant, etc..) will end up using it for things not allowed.

Re: suspended ceiling [Re: renosteinke] #207695 11/20/12 03:23 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
Those small condensate pumps are readily available with a whip, but many of the HVAC guys are reluctant to use the right ones the first time around.


Ghost307
Re: suspended ceiling [Re: harold endean] #207699 11/20/12 07:29 PM
Joined: Jul 2004
Posts: 9,439
G
gfretwell Offline
Member
If you can get them with the MC whip, case closed. I just had never seen one.


Greg Fretwell
Re: suspended ceiling [Re: harold endean] #207708 11/20/12 11:57 PM
Joined: Apr 2002
Posts: 7,133
HotLine1 Offline
Member
That may be a Chicago thing, I have not seen any up here either. I'll ask around next week.

I remember someone saying that there are AHs with a factory single recept installed for a condensate pump; that would solve the problem IMHO.


John
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,592
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
dsk 11
djk 5
Admin 3
Popular Topics(Views)
263,488 Are you busy
198,577 Re: Forum
187,491 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3