ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
nec 110.3 (B)
by gfretwell - 09/22/21 11:11 PM
Grounding electrodes
by gfretwell - 09/07/21 03:41 PM
Looking For Electricians in the Midlands
by Alex247 - 09/06/21 05:26 AM
New in the Gallery:
Now you know.
Now you know.
by Tom_Horne, September 7
February, North East Indiana
February, North East Indiana
by timmp, July 25
Who's Online Now
0 members (), 43 guests, and 25 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#207479 10/31/12 10:39 AM
Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
Hello,

I have a old (1980) portable generator with a 30A, 240V twistlock receptacle (3-prong) with 2 hots and gnd. It also has 120V, 20A receptacle as well on the panel of the generator.

Do I have to run a seperate neutral from panel to the generator and terminate the neutral to the neutral at the generator? Or do I connect the gnd from the generator receptacle to the neutral at the panel?

Thanks in advance

2017 / 2014 NEC & Related Books and Study Guides
Joined: Jul 2004
Posts: 9,663
Likes: 4
G
Member
Are you talking about connecting to the house panel?

Finding the wiring diagram would be helpful. Do you have the instruction manual?

You need to figure out of that 3d prong is the neutral (it probably is), then figure out if it is bonded to the generator frame. That is just a few minutes with your meter.
Use the neutral and the ground on the 120v outlets as references.

If this is the neutral and isolated from the frame you would connect it as a non-SDS supply. The transfer switch will transfer the ungrounded connection and the neutral is a direct connection along with an EGC to the generator frame that you will need to add.


Greg Fretwell
Joined: Jul 2007
Posts: 1,335
S
Member
If it is for a panel that has utility power, it goes to a transfer switch, not to the panel. If the gen don't have neutral, you can't power 120 loads with 240 side


"Live Awesome!" - Kevin Carosa
Joined: Apr 2002
Posts: 7,279
Likes: 3
Member
Just a note of caution!!

YOU must prevent any 'backfeed' to your utility (POCO) wiring. As you profile describes you as an EE, I will suggest you locate a qualified electrical contractor within your local area to connect your generator.

You also must be mindful of the carbon monoxide exhaust fumes from the gen! Three EMS trips to the local hospital today for people who had gens in open door garages.

Be safe


John

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
timmp
timmp
Leo, IN, USA
Posts: 27
Joined: June 2004
Top Posters(30 Days)
timmp 3
Popular Topics(Views)
283,074 Are you busy
216,812 Re: Forum
203,189 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5