Generator Connection #207479 10/31/12 09:39 AM
Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
Hello,

I have a old (1980) portable generator with a 30A, 240V twistlock receptacle (3-prong) with 2 hots and gnd. It also has 120V, 20A receptacle as well on the panel of the generator.

Do I have to run a seperate neutral from panel to the generator and terminate the neutral to the neutral at the generator? Or do I connect the gnd from the generator receptacle to the neutral at the panel?

Thanks in advance

2017 / 2014 NEC & Related Books and Study Guides
Re: Generator Connection [Re: Bravo] #207483 10/31/12 12:46 PM
Joined: Jul 2004
Posts: 9,540
G
gfretwell Offline
Member
Are you talking about connecting to the house panel?

Finding the wiring diagram would be helpful. Do you have the instruction manual?

You need to figure out of that 3d prong is the neutral (it probably is), then figure out if it is bonded to the generator frame. That is just a few minutes with your meter.
Use the neutral and the ground on the 120v outlets as references.

If this is the neutral and isolated from the frame you would connect it as a non-SDS supply. The transfer switch will transfer the ungrounded connection and the neutral is a direct connection along with an EGC to the generator frame that you will need to add.


Greg Fretwell
Re: Generator Connection [Re: Bravo] #207484 10/31/12 12:46 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
If it is for a panel that has utility power, it goes to a transfer switch, not to the panel. If the gen don't have neutral, you can't power 120 loads with 240 side


"Live Awesome!" - Kevin Carosa
Re: Generator Connection [Re: Bravo] #207490 10/31/12 09:22 PM
Joined: Apr 2002
Posts: 7,215
HotLine1 Offline
Member
Just a note of caution!!

YOU must prevent any 'backfeed' to your utility (POCO) wiring. As you profile describes you as an EE, I will suggest you locate a qualified electrical contractor within your local area to connect your generator.

You also must be mindful of the carbon monoxide exhaust fumes from the gen! Three EMS trips to the local hospital today for people who had gens in open door garages.

Be safe


John

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,887 Are you busy
205,750 Re: Forum
193,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3