230-2 states that a structure shall be supplied by only one service. We have an existing commercial building with two services on it. One service supplys the building to which the services are attached, the second service supplys a pedestal on an adjacent property. Both parcels are owned by the same company. The AHJ is refusing a re-connect stating 230-2. I don't see where 230-2 applies, the second service is supplying another structure (the pedestal, it is not supplying the same building as the first service. We do not have two services supplying one building.

Also, 230.3 states service conductors supplying a building or other structure shall not pass thru the interior of another building or structure. The load side conductors of the second service do pass thru the first building, but they are not "service conductors", correct?


2017 / 2014 NEC & Related Books and Study Guides
Re: 230-2 [Re: BigB] #207386
10/24/12 01:19 AM
10/24/12 01:19 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,287
Estero,Fl,usa
Where are the service disconnects?


Greg Fretwell
Re: 230-2 [Re: gfretwell] #207387
10/24/12 01:33 AM
10/24/12 01:33 AM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 732
Tucson, AZ USA
Originally Posted by gfretwell
Where are the service disconnects?


They are both on the first building, side by side.

Re: 230-2 [Re: BigB] #207388
10/24/12 02:41 AM
10/24/12 02:41 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,287
Estero,Fl,usa
Then I say there are 2 services brought to one building, sorry.
Maybe you can get a vote the other way here but the only one that counts is your AHJ.


Greg Fretwell
Re: 230-2 [Re: BigB] #207391
10/24/12 11:08 AM
10/24/12 11:08 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,024
Brick, NJ USA
Are there two (2) utility drops? IF there is one utility drop, or one UG lateral then IMHO it sounds like only one service.


John
Re: 230-2 [Re: HotLine1] #207401
10/24/12 10:06 PM
10/24/12 10:06 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 732
Tucson, AZ USA
Originally Posted by HotLine1
Are there two (2) utility drops? IF there is one utility drop, or one UG lateral then IMHO it sounds like only one service.


Of course, I wasn't thinking since I was pissed off from dealing with the local bureaucracy. There is only one service, just two meter mains. Since I didn't show the drop on my drawing they probably thought there were 2 drops, or else they are just being stupid, and it is rubbing off on me. I will let you know what happens when I point this out. Thanks.

Last edited by BigB; 10/24/12 10:08 PM.
Re: 230-2 [Re: BigB] #207404
10/24/12 10:31 PM
10/24/12 10:31 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,287
Estero,Fl,usa
OK you are right, one service, 2 disconnects and a second building scenario.

It sounds like you just resubmit your plans, say sorry for the confusion and move on. wink


Greg Fretwell
Re: 230-2 [Re: BigB] #207406
10/24/12 10:51 PM
10/24/12 10:51 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 732
Tucson, AZ USA
Part of the problem is our new permit application system, we are using ProjectDox. It is nice in some ways that you can do everything from the office but like everything else on the internet it's not always the same as face to face.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,516
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
sparky 9
Popular Topics(Views)
249,308 Are you busy
187,243 Re: Forum
176,608 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 15 (0.004s) Memory: 0.9940 MB (Peak: 1.1541 MB) Zlib enabled. Server Time: 2018-09-20 14:36:41 UTC