#207302 10/14/12 11:15 PM
Joined: Jan 2004
Posts: 171
M
Merlin Offline OP
Member
Can anyone tell me what the requirements are for explosionproof equipment located outside. I am installing a circuit to a propane transfer pump. The owner want the switch mounted on the outside of an adjacent building located about 18 feet from the tank and pump. Would that switch need to be hazardous rated?

Horizontal Ad
Joined: May 2005
Posts: 984
Likes: 2
G
Member
If you're mounting the switch more than 18" above the ground, you should be okay at that distance. Don't forget to use IMC or GRC and the appropriate sealing fittings for the conduit run.
And I would suggest you run it past your local AHJ just to avoid having to change it after you're all finished with the installation.


Ghost307

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
Popular Topics(Views)
558,633 Are you busy
432,923 Re: Forum
401,932 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5