There is a concern on an existing installation where the meter and outdoor load center are approximately 7 feet from the inside wall of an in ground pool. Looking thru 680 I see no violation, not even a requirement to include it in the equipotential bonding as it is not within 5 feet of the inside wall. Am I correct?
|
|
|
Re: Meter & load center proximity to pool
[Re: BigB]
#206918
09/01/12 12:04 PM
|
Joined: Jul 2004
Posts: 9,571
Member
|
I think you are right but look up. Where is the service drop?
Greg Fretwell
|
|
|
Re: Meter & load center proximity to pool
[Re: gfretwell]
#206919
09/01/12 02:59 PM
|
Joined: Mar 2004
Posts: 778
OP
Member
|
I think you are right but look up. Where is the service drop? The service conductors are piped across the roof for 25 feet then there is a 90 up with a weatherhead. Adjacent to this weatherhead there is a service mast fastened to the building to support the overhead, keeping it 25' from the water. It is not pretty.
|
|
|
Re: Meter & load center proximity to pool
[Re: BigB]
#206920
09/01/12 04:25 PM
|
Joined: Jul 2004
Posts: 9,571
Member
|
It sounds legal tho... sometimes the law ain't pretty  Was any consideration given to raceways on a roof? (derating)
Greg Fretwell
|
|
|
Re: Meter & load center proximity to pool
[Re: gfretwell]
#206924
09/01/12 09:37 PM
|
Joined: Mar 2004
Posts: 778
OP
Member
|
It sounds legal tho... sometimes the law ain't pretty  Was any consideration given to raceways on a roof? (derating) I doubt it since my area just started enforcing derating for ambient last year, and this installation is at least 30 years old. This brings up something I have been wondering about, when de-rating residential service conductors would you start with the ampacities listed in table 310.15(B)(6)?
|
|
|
Re: Meter & load center proximity to pool
[Re: BigB]
#206930
09/02/12 11:51 AM
|
Joined: Jul 2004
Posts: 9,571
Member
|
That is why I was curious. 310.15(B)(2)(c) refers you to 310.16 I am not sure what you do with (B)(6) service feeders. I was wondering what size they ended up with.
Greg Fretwell
|
|
|
|
|