There is a concern on an existing installation where the meter and outdoor load center are approximately 7 feet from the inside wall of an in ground pool. Looking thru 680 I see no violation, not even a requirement to include it in the equipotential bonding as it is not within 5 feet of the inside wall. Am I correct?

2017 / 2014 NEC & Related Books and Study Guides
Re: Meter & load center proximity to pool [Re: BigB] #206918
09/01/12 12:04 PM
09/01/12 12:04 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,336
Estero,Fl,usa
I think you are right but look up. Where is the service drop?


Greg Fretwell
Re: Meter & load center proximity to pool [Re: gfretwell] #206919
09/01/12 02:59 PM
09/01/12 02:59 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 740
Tucson, AZ USA
Originally Posted by gfretwell
I think you are right but look up. Where is the service drop?


The service conductors are piped across the roof for 25 feet then there is a 90 up with a weatherhead. Adjacent to this weatherhead there is a service mast fastened to the building to support the overhead, keeping it 25' from the water. It is not pretty.

Re: Meter & load center proximity to pool [Re: BigB] #206920
09/01/12 04:25 PM
09/01/12 04:25 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,336
Estero,Fl,usa
It sounds legal tho... sometimes the law ain't pretty wink

Was any consideration given to raceways on a roof? (derating)


Greg Fretwell
Re: Meter & load center proximity to pool [Re: gfretwell] #206924
09/01/12 09:37 PM
09/01/12 09:37 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 740
Tucson, AZ USA
Originally Posted by gfretwell
It sounds legal tho... sometimes the law ain't pretty wink

Was any consideration given to raceways on a roof? (derating)


I doubt it since my area just started enforcing derating for ambient last year, and this installation is at least 30 years old. This brings up something I have been wondering about, when de-rating residential service conductors would you start with the ampacities listed in table 310.15(B)(6)?

Re: Meter & load center proximity to pool [Re: BigB] #206930
09/02/12 11:51 AM
09/02/12 11:51 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,336
Estero,Fl,usa
That is why I was curious.
310.15(B)(2)(c) refers you to 310.16
I am not sure what you do with (B)(6) service feeders. I was wondering what size they ended up with.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
andey 3
Popular Topics(Views)
253,205 Are you busy
189,862 Re: Forum
179,563 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 15 (0.007s) Memory: 0.9771 MB (Peak: 1.1269 MB) Zlib enabled. Server Time: 2019-02-16 11:25:32 UTC