Joined: Mar 2004
Posts: 818
B
BigB Offline OP
Member
There is a concern on an existing installation where the meter and outdoor load center are approximately 7 feet from the inside wall of an in ground pool. Looking thru 680 I see no violation, not even a requirement to include it in the equipotential bonding as it is not within 5 feet of the inside wall. Am I correct?

Horizontal Ad
Joined: Jul 2004
Posts: 9,988
Likes: 35
G
Member
I think you are right but look up. Where is the service drop?


Greg Fretwell
Joined: Mar 2004
Posts: 818
B
BigB Offline OP
Member
Originally Posted by gfretwell
I think you are right but look up. Where is the service drop?


The service conductors are piped across the roof for 25 feet then there is a 90 up with a weatherhead. Adjacent to this weatherhead there is a service mast fastened to the building to support the overhead, keeping it 25' from the water. It is not pretty.

Joined: Jul 2004
Posts: 9,988
Likes: 35
G
Member
It sounds legal tho... sometimes the law ain't pretty wink

Was any consideration given to raceways on a roof? (derating)


Greg Fretwell
Joined: Mar 2004
Posts: 818
B
BigB Offline OP
Member
Originally Posted by gfretwell
It sounds legal tho... sometimes the law ain't pretty wink

Was any consideration given to raceways on a roof? (derating)


I doubt it since my area just started enforcing derating for ambient last year, and this installation is at least 30 years old. This brings up something I have been wondering about, when de-rating residential service conductors would you start with the ampacities listed in table 310.15(B)(6)?

Joined: Jul 2004
Posts: 9,988
Likes: 35
G
Member
That is why I was curious.
310.15(B)(2)(c) refers you to 310.16
I am not sure what you do with (B)(6) service feeders. I was wondering what size they ended up with.


Greg Fretwell

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
BigB 4
Popular Topics(Views)
327,864 Are you busy
252,729 Re: Forum
235,353 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5