ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Calling all Non-US members!! (Non-US only)
by HotLine1. 06/13/18 01:50 PM
GE Lighting Recalls LED Tube Lamps
by Admin. 06/12/18 09:32 PM
Ketra Recalls Recessed Downlights
by Admin. 06/12/18 09:17 PM
diazed fuses
by Texas_Ranger. 06/11/18 07:31 AM
soda can fuse from UK, facebook
by wa2ise. 06/06/18 11:02 PM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 22 guests, and 24 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Bond bushings #206734
08/04/12 12:26 PM
08/04/12 12:26 PM
S
SJT  Offline OP
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
In regard to threaded grounding bushings (with grounding lug on it), where are these to be installed?
I was checking 250.97 and 300.4(G) in the code.
If possible, could you refer me to the code sections, where we must install such bushings, as compared to normal bushings?
Just trying to have code references, so we don't install ground bushings where they are not needed.
Thanks - Good day
SJT

2017 / 2014 NEC & Related Books and Study Guides
Re: Bond bushings [Re: SJT] #206739
08/04/12 10:54 PM
08/04/12 10:54 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
The SINGLE most common use for such grounding bushings is at the terminus of an EMT, GRC, IMC, Flex shielded run on a GEC -- wherever its headed.

Sometimes I've installed them as a grounding lug even with a naked bare GEC system bonding conductor.

Other than that, they've got little purpose.

They are never used to replace lazy-lugs/ lay-in lugs.

And they are typically UL listed for conductor size -- maxxed at 3/0 -- the largest GEC from the table.

That's one hint from the manufacturer/ UL as to their purpose -- they're choke eliminators -- and the inspector will be looking for them on all GEC bonding runs that are wrapped in steel pipe/ steel flex.

They are NOT required if the same run is wrapped in PVC.

As for GEC Systems, the NEC Handbook has sweet illustrations. Exhibit 250.32 [ BTW, the bushing is normally attached physically to the raceway -- but it doesn't absolutely have to -- see the diagram.

NEC 250.64.E

NEC 250.104

Happy to post the citations for the forum...

(2005 copy...)


Tesla

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
twh 5
Popular Topics(Views)
247,602 Are you busy
184,935 Re: Forum
174,161 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.005s) Memory: 0.9430 MB (Peak: 1.0603 MB) Zlib enabled. Server Time: 2018-06-20 00:07:57 UTC