Temporary Construction Lighting
#206726
08/03/12 11:09 AM
|
Joined: Jul 2004
Posts: 136
OP
Member
|
What is a typical required light level specified for temporary general construction lighting? I have seen 50FC specified but that seems really high and had to achieve.
|
|
|
Re: Temporary Construction Lighting
[Re: cgw]
#206728
08/03/12 12:46 PM
|
Joined: Jul 2004
Posts: 9,575
Member
|
You are 5x to 10x the real rule, depending on what kind of "construction area" it is 5 FC in general construction areas, 10 FC in batch plants and electrical equipment rooms but as low as 3 FC if you are excavating, placing concrete or storing materials http://www.osha.gov/pls/oshaweb/owadisp.show_document?p_table=STANDARDS&p_id=1063050 FC would be a very brightly lit office.
Greg Fretwell
|
|
|
Re: Temporary Construction Lighting
[Re: cgw]
#206747
08/06/12 12:02 PM
|
Joined: Jul 2004
Posts: 136
OP
Member
|
|
|
|
|
|