RV outlets #206674
07/30/12 10:41 PM
07/30/12 10:41 PM
S
schenimann  Offline OP
Member
Joined: Feb 2008
Posts: 193
Western North Carolina
Our church is wanting to put in some 50 and 30amp outlets for RVs. We have singing groups that bring their large busses and need a hookup so they don't have to run their gens for 2-3 days.

The panels are 208/120 and I need 120/240. Can I use the 208v to operate these outlets or do I need to change it to 240. I understand that many 240v motors have run on 208 for years. What's the best thing to do?

Work Gear for Electricians and the Trades
Re: RV outlets [Re: schenimann] #206676
07/31/12 02:57 AM
07/31/12 02:57 AM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Don't sweat nothing.

The VAST bulk of the true loads are 120VAC...

Only a fraction of the RV load uses two poles: air conditioning in the larger sizes.

So...

Hook up 208Y120 as if it were 240/120 and all will be well.

( No RV uses electric power for hot water at 240VAC, nor do any use electric ranges, etc. )



Tesla
Re: RV outlets [Re: schenimann] #206683
07/31/12 04:06 PM
07/31/12 04:06 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,302
Estero,Fl,usa
Heating elements are not a concern anyway. They just heat less.
The AC units are the heavy hitter in an RV.

Maybe a peek at a few RV manufacturer specs would answer the question.


Greg Fretwell
Re: RV outlets [Re: schenimann] #206687
07/31/12 04:23 PM
07/31/12 04:23 PM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
I can say with certainty that I've been to many RV parks that use 120/208 Wye services and distribute from there. I really don't think you'll have any trouble at all.

My friend has a motor coach RV that has an electric cooktop in it that only uses a 120 volt circuit, as does the washer/dryer combo. I'm with Tesla: You probably won't see many 240 volt loads, if at all in an RV.


---Ed---

"But the guy at Home Depot said it would work."
Re: RV outlets [Re: schenimann] #206694
07/31/12 11:23 PM
07/31/12 11:23 PM
W
WESTUPLACE  Offline
Member
Joined: Mar 2004
Posts: 251
Kingwood, TX USA
I have worked on lots of RVs Most all but the very largest (and most expensive) use 120v for everything just divided across 2 ckts a very few use dryers that are 240v and fewer use 240V AC units. Most all rooftop AC units are 120v. I see no problem using 120/208.

Re: RV outlets [Re: schenimann] #206887
08/24/12 06:50 PM
08/24/12 06:50 PM
S
sabrown  Offline
Member
Joined: Dec 2002
Posts: 304
Ogden, Utah, USA
If you have a handbook look at 2011 NEC 551.40(A). It basically says that equipment be rated 208-230 to allow for 208Y/120 distribution.

Shane


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
251,518 Are you busy
188,690 Re: Forum
178,391 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.433s Queries: 15 (0.039s) Memory: 0.9768 MB (Peak: 1.1257 MB) Zlib enabled. Server Time: 2018-11-17 02:35:02 UTC