New Fire Alarm Conduit #206459
07/04/12 07:03 PM
07/04/12 07:03 PM
S
Steve Miller  Offline OP
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
Need opinions here:
We are having a new Fire Alarm installed in one of our buildings. Some of the new Fire Alarm EMT is installed above the bar joists, tight to the roof deck. We're on 2008. I've been thru 760 several times and can find no ref to 300.4. Therefore I need opinions:
Based on this section
760.3 Other Articles. Circuits and equipment shall comply
with 760.3(A) through (G). Only those sections of Article
300 referenced in this article shall apply to fire alarm
systems.
Does this section apply?
(E) Cables and Raceways Installed Under Roof Decking.
A cable- or raceway-type wiring method, installed in
exposed or concealed locations under metal-corrugated sheet
roof decking, shall be installed and supported so the nearest
outside surface of the cable or raceway is not less than
38 mm (11⁄2 in.) from the nearest surface of the roof decking.

2017 / 2014 NEC & Related Books and Study Guides
Re: New Fire Alarm Conduit [Re: Steve Miller] #206462
07/04/12 11:55 PM
07/04/12 11:55 PM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 6,950
Brick, NJ USA
Steve:

I feel your pain after a quick read. Although 300.4 SHOULD apply, there is no written word that I see.

IMHO, I would have a man to man with the installer, explaining the theory behind 300.4, and ask for voluntary compliance.

This is one of the 'holes' that needs to be plugged. Thank you for pointing this out.





Last edited by HotLine1; 07/05/12 10:38 PM. Reason: corrected name

John
Re: New Fire Alarm Conduit [Re: Steve Miller] #206468
07/05/12 09:57 PM
07/05/12 09:57 PM
S
Steve Miller  Offline OP
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
I'm hoping the AHJ will enforce 300.4. My installer already told me no way.

Re: New Fire Alarm Conduit [Re: Steve Miller] #206469
07/05/12 10:39 PM
07/05/12 10:39 PM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 6,950
Brick, NJ USA
IF your installer is really 'code savy', he may take the stand that 300.4 does not apply, based on 760.

Between a rock & a hard place.


John
Re: New Fire Alarm Conduit [Re: Steve Miller] #206471
07/06/12 04:21 AM
07/06/12 04:21 AM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
And what of the Exclusion for EMT RMC IMC ?


Tesla
Re: New Fire Alarm Conduit [Re: Steve Miller] #206475
07/06/12 10:21 AM
07/06/12 10:21 AM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 6,950
Brick, NJ USA
Tesla:

Where are you referencing your exclusion??

RMC/IMC are allowed in 300.4(E)


John
Re: New Fire Alarm Conduit [Re: Steve Miller] #206478
07/07/12 04:52 AM
07/07/12 04:52 AM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
AND EMT...

So no problem...

Get it?

So the installer 'wins' the argument.

Last edited by Tesla; 07/07/12 04:53 AM.

Tesla
Re: New Fire Alarm Conduit [Re: Steve Miller] #206479
07/07/12 01:52 PM
07/07/12 01:52 PM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 6,950
Brick, NJ USA
Tesla:

Am I missing something? Where is EMT mentioned?

From 2011 NEC 300.4
(E) Cables, Raceways, or Boxes Installed in or Under
Roof Decking. A cable, raceway, or box, installed in exposed
or concealed locations under metal-corrugated sheet
roof decking, shall be installed and supported so there is
not less than 38 mm (11⁄2 in.) measured from the lowest
surface of the roof decking to the top of the cable, raceway,
or box. A cable, raceway, or box shall not be installed in
concealed locations in metal-corrugated, sheet decking–
type roof.
Informational Note: Roof decking material is often repaired
or replaced after the initial raceway or cabling and
roofing installation and may be penetrated by the screws or
other mechanical devices designed to provide “hold down”
strength of the waterproof membrane or roof insulating
material.
Exception: Rigid metal conduit and intermediate metal
conduit shall not be required to comply with 300.4(E).


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 222
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
245,928 Are you busy
182,996 Re: Forum
172,781 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.033s Queries: 15 (0.005s) Memory: 0.9948 MB (Peak: 1.1595 MB) Zlib enabled. Server Time: 2018-04-25 18:35:19 UTC