ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Pull out fuse panel?
by gfretwell. 12/17/18 02:33 PM
Video door bell causing chime activation of coil
by gfretwell. 12/16/18 09:01 PM
Conduit fill Calculations
by gfretwell. 12/08/18 08:39 PM
Swimming Pool question
by HotLine1. 12/05/18 12:37 PM
Tingle off the water spigot
by rmiell. 11/30/18 01:03 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 38 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
600V single phase 2-wire #206409
06/29/12 01:39 PM
06/29/12 01:39 PM
N
Napo  Offline OP
New Member
Joined: Jun 2012
Posts: 1
Alberta
If you are running a 50mm DB2 underground conduit, for a 2-wire, single phase 600V system (no neutral) between two lighting panels (which have a 600V to 120V transformer) is it mandatory to run a third wire as bonding conductor(to ground)?

The panel themselves have their own grounding electrodes.
The 600V circuits are #2Cu, so in general the code would call for a #6 bonding conductor.

What is the CEC rule/subrule that would make the bonding conductor mandatory? I am not sure I read 10-106 properly.

Tools for Electricians:
Re: 600V single phase 2-wire [Re: Napo] #206410
06/29/12 02:07 PM
06/29/12 02:07 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
You do have to install a bonding wire with the 600 volt wires so if a fault occurs on the primary side that the upstream breaker can trip. The secondary side has a new ground and bonding jumper to serve the 120 volt side.
There are some cases where you can save on the bonding wire but not this case.
When you feed an out building and create a new service entry the neutral can act as the bonding and as the grounded circuit conductor but because the 2 systems are electrically isolated the 600 volt side needs a bonding wire to return fault current to its source but not for the secondary which works like a new service.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,272 Are you busy
189,222 Re: Forum
178,910 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.038s Queries: 15 (0.005s) Memory: 0.9431 MB (Peak: 1.0593 MB) Zlib enabled. Server Time: 2018-12-18 13:11:14 UTC