Fire source!
#206347
06/17/12 08:45 PM
|
Joined: Apr 2002
Posts: 7,225
OP
Member
|
This was the cause. Power strip, one to three adaptors, zip cord extension cords... ![[Linked Image]](https://www.electrical-contractor.net/forums/gallery/24/full/386.jpg)
John
|
|
|
Re: Fire source!
[Re: HotLine1]
#206350
06/18/12 01:02 AM
|
Joined: Jul 2004
Posts: 783
Member
|
What were the loads plugged into this?
|
|
|
Re: Fire source!
[Re: HotLine1]
#206353
06/18/12 02:29 PM
|
Joined: Apr 2002
Posts: 7,225
OP
Member
|
I only saw a fish tank (aquarium), but there had to be other items. Damage: scorched wall; fish tank; 4' hole in ceiling by FD; water/smoke. No visable damage to the receptacle this was plugged into.
John
|
|
|
Re: Fire source!
[Re: HotLine1]
#206354
06/18/12 04:59 PM
|
Joined: Jul 2004
Posts: 9,556
Member
|
This is a nice one ![[Linked Image from gfretwell.com]](http://gfretwell.com/electrical/Need%20an%20extra%20receptacle.jpg)
Greg Fretwell
|
|
|
Re: Fire source!
[Re: HotLine1]
#206355
06/18/12 06:21 PM
|
Joined: Apr 2002
Posts: 7,225
OP
Member
|
John
|
|
|
Re: Fire source!
[Re: gfretwell]
#206359
06/19/12 01:01 AM
|
Joined: Jul 2004
Posts: 783
Member
|
Let me guess.
Continental US.
Public area. Probably flea market.
Powering up "temporary" food vendors.
How close am I?
|
|
|
Re: Fire source!
[Re: LarryC]
#206360
06/19/12 03:39 AM
|
Joined: Jul 2007
Posts: 1,335
Member
|
Kinda look like what I grew up in... I wonder the place I grew up predisposition me be a sparky?
"Live Awesome!" - Kevin Carosa
|
|
|
Re: Fire source!
[Re: HotLine1]
#206431
07/01/12 10:34 PM
|
Joined: Feb 2009
Posts: 1
New Member
|
Power strips typically contain MOVs (metal oxide varistors) for surge suppression. When an MOV ages, its trigger voltage can drop below the peak to peak line voltage, causing it to draw current and heat up. If the power strip has a plastic housing, the burning MOV can set the plastic on fire.
Another bad practice is the "3 way" surge configuration that places MOVs line-to-neutral, line-to-ground and neutral-to-ground. This is strictly for marketing to the dumb masses who think that more is always better. Dumping surge current into the protective ground pulls it off of ground potential. Since this is the zero volt reference for sensitive electronic equipment, bad things can happen (like fried serial ports).
Typically, the neutral-to-ground MOV has an extremely low trigger voltage, so that a loss of neutral will cause it to try to pass the full circuit load current to ground. Obviously, it then burns up.
I worked in an office with modular furniture. Some amateur electricians did not get the wiring harness connectors securely locked together. Over time, they would separate, and when the neutral connection was broken, power strips would melt all over the place. Disassembly revealed it was always caused by a burned neutral-to-ground MOV. One time, a power strip actually broke out in flames. Someone hit it with a fire extinguisher before we got to find out if the sprinkler system worked.
In conclusion, I will bet dollars to donuts that the fire was caused by an MOV, not an overload. Most power strips have a resettable circuit breaker to protect against overload.
BTW, if you want serious surge suppression, put a UL-approved surge suppressor on the service entrance and look at zerosurge.com for point of use protection. They are one of the few companies that make surge suppressors that actually work. No, I am not affiliated in any way with this company.
|
|
|
Re: Fire source!
[Re: HotLine1]
#206444
07/02/12 09:09 PM
|
Joined: Apr 2002
Posts: 7,225
OP
Member
|
Bavmar:
Welcome to ECN, and thanks fo te input.
Last I heard from the FD was 'inproper use of extension cords, adapters, & power strip' was the cause.
John
|
|
|
Re: Fire source!
[Re: HotLine1]
#207693
11/20/12 02:02 AM
|
Joined: Feb 2004
Posts: 1,437
Member
|
A lot of aquarium equipment will state in the instructions not to use a power strip. I've witnessed the reason why at a service call... Condensate will tend to gather on the power cords sometimes and roll down the wire and into the power strip or extension cord. I think the mfr's thinking was that plugging directly into the wall outlet will keep a drip loop in the wire...
|
|
|
|
|