Hello,
If I have a 60 AMP panel or device on 60 AMP breaker, and the wires are 2/0 RW90XLPE feeding the panel or device, do I size the ground for panel or bond for device by the wire size or by the panel rating/breaker size or, if it's a device, by the breaker size of that device?

I know for a panel, min size for ground is #6. So for the 60 AMP panel, I'd need at least that. But that is still well below the size needed to ground 2/0 rated wire.
Or a bond for 2/0 rated wire running from a 60 AMP breaker to a device.

I just don't know if I am supposed to size grounding or bonding by the size of wire ran or the breaker it is on. I would hope by the breaker size.

Horizontal Ad
Joined: Aug 2002
Posts: 402
J
Member
If you use table 16 it is based on the 'largest ungrounded conductor in the circuit..." not on the panel size or overcurrent protection.

Last edited by jdevlin; 05/31/12 09:30 AM.

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
554,834 Are you busy
429,076 Re: Forum
398,876 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5