Joined: Sep 2006
Posts: 155
C
Member
I'm doing a service change at a Cal. house that has had all its 2 wire K&T recept.s swapped for ungrounded 3wire recept....Will a combo Afci/Gfci bkr meet with no equipment ground label. or do I have to put gfci prot label as well, HO is trying to sell house, or do I talk him into replacing with non-ground TR's 2010 CEC, thanks Chris I have not done any rewiring ex. refeed the closet fuse box to splices only. C

2017 / 2014 NEC & Related Books and Study Guides
Joined: Sep 2006
Posts: 155
C
Member
My question is will a combo afci/gfci breaker meet the gfci req. for replaced receptacles on K&T circuits, also has anyone seen tamper resist. 2-wire recept.s

Joined: Apr 2002
Posts: 7,283
Likes: 3
Member
I have not seen any TR two wire receptacles, and none are in the P&S literature I have.

I have to ask....why TR?? Is that a CEC thing?


John
Joined: Sep 2006
Posts: 155
C
Member
My question is will a combo afci/gfci breaker meet the gfci req. for replaced receptacles on K&T circuits, also has anyone seen tamper resist. 2-wire recept.s

Joined: Sep 2006
Posts: 155
C
Member
Oh the Inspector has stated on a corr. notice that recept.s be two-wire of TR type, for all replaced knob and tube outlets. The Homeowner bought the place with the plugs already replaced, I guess it passed the selling inspection 13 years ago when he bought it. He's now trying to make the service safer instead of being in a cabinet at grade with the gas meter, opened a can of worms

Joined: Sep 2006
Posts: 155
C
Member
or gfci protected and labeled no eq. ground, gfci prot.,

Joined: Jul 2004
Posts: 9,672
Likes: 7
G
Member
I think a GFCI breaker would allow replacement with the TR 5-15s.
406.3(D)(3)(c) in 2008 406.3(D)(2)(c) in 2011

Quote
(c) A non–grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked “GFCI Protected” and “No Equipment Ground.” An equipment grounding conductor shall not be connected between the grounding-type receptacles.



The requirement for AFCI would be a local call. A breaker incorporating both should work

The 2011 code requires this effective 1/1/14
406.3(D)(4)


Greg Fretwell
Joined: Sep 2006
Posts: 155
C
Member
thanks greg, I do believe he was stating the 2008 code for TR recept.s but also didnt write a correction but said all convenience receptacles should be afci protected. but that was for new circuits, and all I've run are circuits to refeed the old fuse panel,

Joined: Jul 2004
Posts: 9,672
Likes: 7
G
Member
AFCI on old work seems to be all over the place depending on how your "rehab/existing building" codes are written and what your AHJ wants. I usually avoid trying to guess what the local guys want. If the 2011 is adopted and they leave 406.3 intact a lot of that indecision will go away. You will be doing AFCI and GFCI on any replacements after 1/1/14 the way I read it.


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Top Posters(30 Days)
Admin 3
dsk 2
Popular Topics(Views)
286,517 Are you busy
218,948 Re: Forum
205,072 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5