ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Old POCO Letter
Old POCO Letter

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 22 guests, and 26 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#206120 05/27/12 07:01 AM
Joined: Mar 2005
Posts: 1,803
Member
I have some GU5.3 12v dichroic halogen luminaires [5 x 20W in a string suspended on a pair of catenary cables]. These are fitted in a utility room. I avoided low energy bulbs because of the lights being switched on and off regularly as we pop in to tend the machines. Yesterday I hung a row of wall cabinets, and spent a couple of hours in there fitting them and hanging the doors. The bulbs noticeably dimmed during this time. The 230v-12v transformer is a big wirewound unit, not electronic, and it got quite hot. Once it cooled off, normal output resumed. Anyone else noticed this problem?


Wood work but can't!
Horizontal Ad
Joined: Jul 2004
Posts: 10,004
Likes: 36
G
Member
What is the rating of the transformer?


Greg Fretwell
Joined: Jul 2004
Posts: 787
L
Member
Hang a voltmeter off of the transformer output terminals to see if the output voltage sags as the transformer heats up. If it does, check the input voltage to determine if it is sagging too.

The heat could be from overloading the transformer or a high resistance connection(s).

New thought: Is the transformer a 60 Hz transformer? Running a 60 Hz transformer on 50 Hz will cause it to over heat due to less inductive reactance. It is the same reason 60 Hz motors operated on 50 Hz run much hotter.

Joined: Dec 2002
Posts: 206
G
Member
I would suspect that your transformer is marginally rated for the load you have on it. Think temerature coefficients.
As the transformer temperature rises so does the winding resistance, hence reducing the output voltage.
As the lamps consequently dim and the filaments cool their resistance will reduce, so increasing load. I think I can visualise a potential runaway effect here which could kill the transformer.

Joined: Mar 2005
Posts: 1,803
Member
It's rated 105VA, 12V output, 230v 50hz, with 5 x 20W bulbs. Made in France, BTW. I have 3 of these units in various locations. No probs with the other two, tested today. I'll check out the wiring tomorrow.


Wood work but can't!
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
100 watts at 12 volts is 8 amps. If a connection was even half an ohm, it would drop a couple volts.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,476
Joined: January 2005
Top Posters(30 Days)
Popular Topics(Views)
337,955 Are you busy
263,105 Re: Forum
243,392 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5