sub panel in elevator shaft #205961 05/02/12 01:31 AM
Joined: May 2012
Posts: 13
S
sidmuer Offline OP
Member
Hello.
I am trying to find some info, and seem to be hitting a wall.
I was wondering if anyone here knew the min subpanel height in an elevator shaft?
And if no min, what would the maximum be?

Thanks.

Tools for Electricians:
Re: sub panel in elevator shaft [Re: sidmuer] #205962 05/02/12 05:12 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
In my state, California, elevators are regulated at the state level -- with special almighty inspectors.

They'd never permit such a beast in the first place, at what ever height you care to posit.

Elevator regulation overrides the NEC -- and is much, much more restrictive.


Tesla
Re: sub panel in elevator shaft [Re: sidmuer] #205963 05/02/12 06:05 PM
Joined: May 2012
Posts: 13
S
sidmuer Offline OP
Member
I was also thinking, along the lines if this just not being permisible.
Especially in the case of an emergency, you'd want easy access.

I guess, at this point, I will assume it is just not possible.

Last edited by sidmuer; 05/02/12 06:06 PM.
Re: sub panel in elevator shaft [Re: sidmuer] #205964 05/02/12 07:52 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
You cannot put any building services in an elevator shaft unless it is for the elevators. This is not much at all. Smoke detector, pit light and pit receptacle. I have done more than 1 service call to remove electrical installations that used the elevator shaft as a riser ie only emt and 3 wires were in the pipe.
Now for the mechanical room you need permission from the elevator inspector to put anything more than the electrical for the elevator. Even a jb can be refused if it is not associated with the operation of the elevator. So a disconnect for the car and a disconnect for the car light. a light and switch for the room and a plug for the elevator service guys. Fire alarm device. All other equipment is by the elevator company.

So a panel? No way. even the disco for the elevator has to have a pilot switch that operates from the opening of the main disconnect and a panel won't work for that either.

Re: sub panel in elevator shaft [Re: mikesh] #205966 05/02/12 11:32 PM
Joined: May 2012
Posts: 13
S
sidmuer Offline OP
Member
Thanks Mikesh!
It is actually a test question. Although I do not know if I have read it correct (bad memory??) But if my bad memory is correct, the question was: What's the min height of a sub-panel in an elevator shaft?
I would assume the sub-panel is for the elevator. But by the looks of it, even a sub-panel for the elevator is not allowed in the shaft. Correct?

Originally Posted by mikesh
You cannot put any building services in an elevator shaft unless it is for the elevators. This is not much at all. Smoke detector, pit light and pit receptacle. I have done more than 1 service call to remove electrical installations that used the elevator shaft as a riser ie only emt and 3 wires were in the pipe.
Now for the mechanical room you need permission from the elevator inspector to put anything more than the electrical for the elevator. Even a jb can be refused if it is not associated with the operation of the elevator. So a disconnect for the car and a disconnect for the car light. a light and switch for the room and a plug for the elevator service guys. Fire alarm device. All other equipment is by the elevator company.

So a panel? No way. even the disco for the elevator has to have a pilot switch that operates from the opening of the main disconnect and a panel won't work for that either.

Re: sub panel in elevator shaft [Re: sidmuer] #205971 05/03/12 06:23 PM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
FYI, that will not fly down here in NJ either!


John
Re: sub panel in elevator shaft [Re: sidmuer] #205972 05/03/12 08:02 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
Test question?

My answer would be only materials directly associated with the elevator may be in the shaft plus the smoke detector.
From 38-005 the minimum headroom is 2000mm but that is for controllers, disconnecting means but not panelboards which I would prohibit under 6-206 locating a panel in a hoistway should anyone think it is an acceptable location.

Re: sub panel in elevator shaft [Re: sidmuer] #205986 05/06/12 08:22 AM
Joined: May 2012
Posts: 13
S
sidmuer Offline OP
Member
thanks guys! Obviously a trick question.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,453 Are you busy
209,361 Re: Forum
196,636 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3