Unequal tapping of a dual primary transformer. #205909 04/23/12 02:16 PM
Joined: Jul 2004
Posts: 783
L
LarryC Offline OP
Member
Question for you folks.

I have some dual primary / dual secondary transformers with a voltage tap on the primary windings. The primaries are wound for 120 V with a tap at 100 Volts. If I want to use them at full rated power and my supply voltage was 220 V, would I run into issues if I series the primaries with one wired for 120 V and other on wired for 100 Volts?

The units are AMVECO MT3750DS torroids.

Thanks.

Larry C

Work Gear for Electricians and the Trades
Re: Unequal tapping of a dual primary transformer. [Re: LarryC] #205910 04/23/12 02:49 PM
Joined: Dec 2002
Posts: 204
G
geoff in UK Offline
Member
I wouldn't forsee any problem with what you propose, provided the transformer is designed to give "full rated power" when used on the 100v taps.
Its just like having one primary tapped 100/120/220/240.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,601 Are you busy
209,519 Re: Forum
196,888 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3