Joined: Jul 2004
Posts: 783
L
LarryC Offline OP
Member
Question for you folks.

I have some dual primary / dual secondary transformers with a voltage tap on the primary windings. The primaries are wound for 120 V with a tap at 100 Volts. If I want to use them at full rated power and my supply voltage was 220 V, would I run into issues if I series the primaries with one wired for 120 V and other on wired for 100 Volts?

The units are AMVECO MT3750DS torroids.

Thanks.

Larry C

Joined: Dec 2002
Posts: 205
G
Member
I wouldn't forsee any problem with what you propose, provided the transformer is designed to give "full rated power" when used on the 100v taps.
Its just like having one primary tapped 100/120/220/240.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,287
Joined: December 2000
Top Posters(30 Days)
timmp 3
Popular Topics(Views)
282,928 Are you busy
216,696 Re: Forum
203,120 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5