ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
dsk 13
Admin 4
Recent Posts
electircal ageing test on IPC
by SIAME. 08/15/17 02:43 AM
electrical aging test on IPC
by gfretwell. 08/15/17 12:27 AM
Bathroom electrical
by gfretwell. 08/14/17 02:05 AM
"Line level" audio on Cat 5?
by gfretwell. 08/08/17 10:39 PM
Fire alarm phone lines and color coding
by gfretwell. 08/08/17 10:26 PM
New in the Gallery:
Housebilding DIY wiring
Popular Topics(Views)
239,891 Are you busy
175,467 Re: Forum
167,743 Need opinion
Who's Online Now
0 registered members (), 27 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#205675 - 03/21/12 01:21 PM Conduit fill  
Willie  Offline
New Member
Joined: Mar 2012
Posts: 7
BC Canada
In a 200 amp residential application can I put 3 conductors of 4/0 and 1 conductor of # 6 into a 2 inch EMT. I am using RW90/X link Aluminum.


Tools for Electricians:

#205678 - 03/21/12 05:28 PM Re: Conduit fill [Re: Willie]  
dougwells  Offline


Member
Joined: May 2003
Posts: 1,138
kamloops BC Canada
Why the #6 ? it this the lateral between the Meter Socket/base and the main disconnect for the Service Panel ??


#205680 - 03/21/12 08:37 PM Re: Conduit fill [Re: dougwells]  
Willie  Offline
New Member
Joined: Mar 2012
Posts: 7
BC Canada
Yes, it's a five run with an LB and 4 weather tight connectors between the meter socket & the disconnect switch. I am thinking the # 6 may be a requirement of the CEC although the ground rods should be connected to the disconnect switch I think.


#205682 - 03/22/12 01:22 AM Re: Conduit fill [Re: Willie]  
Willie  Offline
New Member
Joined: Mar 2012
Posts: 7
BC Canada
I should add the bare # 6 is to ensure the meter base remains at ground potential even if the LB and related exterior fittings loosen over time. In the meter cabinet there is a ground lug and I am using a ground bushing on the EMT inside the building. BTW, I am using a ground plate, not rods as previously posted.


#205686 - 03/22/12 02:26 PM Re: Conduit fill [Re: Willie]  
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
The conduit fill is fine but the #6 is not required and will be of little value in a fault. the service pipe gets a bond bushing and the neutral is bonded in the meter base and again at the main switch so adding a #6 only parallels the neutral and the service raceway. I would only add a bond wire if I used PVC as the service raceway even though the neutral meets the minimum code for bonding the meter and mast to the panel. Many inspectors would insist on a bond wire if PVC was used between the meter and panel but it is not required as the grounded service conductor serves both purposes until the neutral bus in the main panel.


#205701 - 03/23/12 01:15 AM Re: Conduit fill [Re: Willie]  
Willie  Offline
New Member
Joined: Mar 2012
Posts: 7
BC Canada
mikesh, I appreciate your answer, I always agreed with everyone that the number 6 is NOT a code requirement. My only question was IF it was requested by the local AHJ would I need to upsize the 2 inch conduit as I could not find an actual code reference. The thought of having to change out the conduit (maybe) did not sit well with me. There is a little more to this story but it is no longer relevant as you have answered my question. THANKS to you and dougwells for the feedback. Case closed.


#206183 - 06/01/12 11:11 PM Re: Conduit fill [Re: Willie]  
JaredRoch  Offline
New Member
Joined: Jan 2012
Posts: 6
Winnipeg MB
10-814(f) i think says that your EMT will be your bond


#206184 - 06/01/12 11:12 PM Re: Conduit fill [Re: Willie]  
JaredRoch  Offline
New Member
Joined: Jan 2012
Posts: 6
Winnipeg MB
and also, if you had to add the number 6 to your conduit, than you would have to follw the steps from Tables 8, 9 and 10 in order to find your conduit size



Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.002s) Memory: 0.7924 MB (Peak: 0.9543 MB) Zlib enabled. Server Time: 2017-08-18 07:08:42 UTC