ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 205 guests, and 28 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Nov 2008
Posts: 13
S
Member
Anyone have some suggestions on how to properly terminate larger wires in panels? I'm faced with a 200A panel but we are sub feeding a seperate 100A panel on the second floor of the house. 3C #2 AL NMD cable is what we used. The problem now is that the neutral busbar has all the same size holes to terminate and they are all only good for up to #4. The panel is an Eaton Cuttler Hammer.

Joined: Jul 2007
Posts: 1,335
S
Member
Granted, Canadian code may have something to say on it. Most neutral busses allow a lug kit to be installed to allow a bigger wire to be terminated on them


"Live Awesome!" - Kevin Carosa
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
Yup, what he said. They make a big lug with a couple of legs that grab 2 slots. Look in the accessory catalog for your panel.


Greg Fretwell
Joined: Mar 2007
Posts: 101
M
Member
I agree with sparkyinak use a lug kit for that panel so long as the panel is rated for a subpanel.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5