Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
The commentary after 517.13(A)
reads "the second component in this approach is the separate insulated grounding conductor required by 517.13 (B. therefore, the metal raceway or metal cable or sheath must qualify as an equipment grounding conductor in accordance with 250.118, INDEPENDENT of any separate wire-type equipment grounding conductor."
Shouldn't it read "in addition to?" The way it reads seems to require the insulated conductor to be isolated back to the the panel and not bonded in the box as a parallel grounding method.

2017 / 2014 NEC & Related Books and Study Guides
Joined: Apr 2002
Posts: 7,282
Likes: 3
Member
Point made & taken. Perhaps a 'bad' use of the word 'independent'.

Logic, is an insulated EGC and an approved metalic wiring method.



John
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
Thanks for the affirmation John.

Joined: Apr 2002
Posts: 7,282
Likes: 3
Member
It would be interesting to see if we get any other responses. Maybe George? Greg?


John
Joined: Mar 2003
Posts: 849
Y
Member
Doesn't 250.48 Cover that??Since its not referred to as an
isolated ground as in 250.146(D)
Yoopersup

Joined: Mar 2003
Posts: 849
Y
Member
Should be 250.148 Not 250.48 Opps

Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
Thanks Yoop
Yes,It's standard procedure to crimp the grounds together and land them in the box that contains a non I.G. device or a splice. In using the dictionary definition below, the wording in the NEC commentary is correct. Both systems can still be referred to as functionally independent even though they are connected. I now know that independent does not necessarily mean separate. Live and learn huh!!


Independent: Not dependent on anything else for function, validity, etc.; separate two independent units make up this sofa


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Top Posters(30 Days)
dsk 6
Popular Topics(Views)
284,715 Are you busy
217,341 Re: Forum
203,693 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5