517.13 (A)Care Facility Grounding #204952 01/24/12 11:59 AM
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
The commentary after 517.13(A)
reads "the second component in this approach is the separate insulated grounding conductor required by 517.13 (B. therefore, the metal raceway or metal cable or sheath must qualify as an equipment grounding conductor in accordance with 250.118, INDEPENDENT of any separate wire-type equipment grounding conductor."
Shouldn't it read "in addition to?" The way it reads seems to require the insulated conductor to be isolated back to the the panel and not bonded in the box as a parallel grounding method.

2017 / 2014 NEC & Related Books and Study Guides
Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204956 01/24/12 09:22 PM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
Point made & taken. Perhaps a 'bad' use of the word 'independent'.

Logic, is an insulated EGC and an approved metalic wiring method.



John
Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204969 01/25/12 10:24 PM
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
Thanks for the affirmation John.

Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204970 01/25/12 10:56 PM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
It would be interesting to see if we get any other responses. Maybe George? Greg?


John
Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204971 01/25/12 11:29 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
Doesn't 250.48 Cover that??Since its not referred to as an
isolated ground as in 250.146(D)
Yoopersup

Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204972 01/25/12 11:30 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
Should be 250.148 Not 250.48 Opps

Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204977 01/26/12 02:02 AM
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
Thanks Yoop
Yes,It's standard procedure to crimp the grounds together and land them in the box that contains a non I.G. device or a splice. In using the dictionary definition below, the wording in the NEC commentary is correct. Both systems can still be referred to as functionally independent even though they are connected. I now know that independent does not necessarily mean separate. Live and learn huh!!


Independent: Not dependent on anything else for function, validity, etc.; separate two independent units make up this sofa


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,453 Are you busy
209,361 Re: Forum
196,636 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3