517.13 (A)Care Facility Grounding #204952
01/24/12 12:59 PM
01/24/12 12:59 PM
W
wewire2  Offline OP
Member
Joined: Nov 2002
Posts: 244
California
The commentary after 517.13(A)
reads "the second component in this approach is the separate insulated grounding conductor required by 517.13 (B. therefore, the metal raceway or metal cable or sheath must qualify as an equipment grounding conductor in accordance with 250.118, INDEPENDENT of any separate wire-type equipment grounding conductor."
Shouldn't it read "in addition to?" The way it reads seems to require the insulated conductor to be isolated back to the the panel and not bonded in the box as a parallel grounding method.

2017 / 2014 NEC & Related Books and Study Guides
Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204956
01/24/12 10:22 PM
01/24/12 10:22 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,094
Brick, NJ USA
Point made & taken. Perhaps a 'bad' use of the word 'independent'.

Logic, is an insulated EGC and an approved metalic wiring method.



John
Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204969
01/25/12 11:24 PM
01/25/12 11:24 PM
W
wewire2  Offline OP
Member
Joined: Nov 2002
Posts: 244
California
Thanks for the affirmation John.

Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204970
01/25/12 11:56 PM
01/25/12 11:56 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,094
Brick, NJ USA
It would be interesting to see if we get any other responses. Maybe George? Greg?


John
Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204971
01/26/12 12:29 AM
01/26/12 12:29 AM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
Doesn't 250.48 Cover that??Since its not referred to as an
isolated ground as in 250.146(D)
Yoopersup

Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204972
01/26/12 12:30 AM
01/26/12 12:30 AM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
Should be 250.148 Not 250.48 Opps

Re: 517.13 (A)Care Facility Grounding [Re: wewire2] #204977
01/26/12 03:02 AM
01/26/12 03:02 AM
W
wewire2  Offline OP
Member
Joined: Nov 2002
Posts: 244
California
Thanks Yoop
Yes,It's standard procedure to crimp the grounds together and land them in the box that contains a non I.G. device or a splice. In using the dictionary definition below, the wording in the NEC commentary is correct. Both systems can still be referred to as functionally independent even though they are connected. I now know that independent does not necessarily mean separate. Live and learn huh!!


Independent: Not dependent on anything else for function, validity, etc.; separate two independent units make up this sofa


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 99
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
257,005 Are you busy
192,881 Re: Forum
182,511 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.005s) Memory: 0.9851 MB (Peak: 1.1403 MB) Zlib enabled. Server Time: 2019-07-17 12:38:48 UTC