AFCI Breaker tripping #203678 10/19/11 09:47 AM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
Has anyone ever had a problem with a Powerline AV Ethernet Adapter Kit tripping an AFCI breaker. I rewired a home and there is one in the basement and one in the bedroom and these 2 areas have these devices. Essentially these things provide ethernet network connectivity at any wall receptacle. Everytime the homeowner does large downloads the AFCI breaker trips.

Work Gear for Electricians and the Trades
Re: AFCI Breaker tripping [Re: sandro2] #203683 10/19/11 12:46 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
I bet it is tripping for a ground fault. If this thing plugs in, try it in a SABC or bathroom circuit and see if it trips the GFCI.
Ethernet cables are supposed to be isolated from the DC bus with transformers but YMMV. The DC ground in a PC is tied to AC ground via the base plate of the PC case through the power supply.


Greg Fretwell
Re: AFCI Breaker tripping [Re: gfretwell] #203685 10/19/11 01:28 PM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
The whole concept of this device is to use the electrical wiring to pass data to the router. It doesnt trip right away it trips only when they start downloading large files. Its weird because they also have one in the basement and that AFCI breaker trips also when they start data transfer.

Re: AFCI Breaker tripping [Re: sandro2] #203686 10/19/11 02:13 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
I would gander that the high frequency two-way data communication is likely screwing with the electronics in the AFCI itself. I'm guessing they were probably only designed to be used with 60Hz, so here is possibly another application from advances in new technology that AFCI’s were never intended to handle.


I would shoot the circuit breaker manufacturer an email so they can begin to make revisions to the next generation of AFCI and add another $20.00 on to the current price for their efforts. frown


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,741 Are you busy
209,655 Re: Forum
197,002 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3