#203678 10/19/11 09:47 AM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
Has anyone ever had a problem with a Powerline AV Ethernet Adapter Kit tripping an AFCI breaker. I rewired a home and there is one in the basement and one in the bedroom and these 2 areas have these devices. Essentially these things provide ethernet network connectivity at any wall receptacle. Everytime the homeowner does large downloads the AFCI breaker trips.

Joined: Jul 2004
Posts: 9,790
Likes: 14
G
Member
I bet it is tripping for a ground fault. If this thing plugs in, try it in a SABC or bathroom circuit and see if it trips the GFCI.
Ethernet cables are supposed to be isolated from the DC bus with transformers but YMMV. The DC ground in a PC is tied to AC ground via the base plate of the PC case through the power supply.


Greg Fretwell
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
The whole concept of this device is to use the electrical wiring to pass data to the router. It doesnt trip right away it trips only when they start downloading large files. Its weird because they also have one in the basement and that AFCI breaker trips also when they start data transfer.

Joined: Nov 2007
Posts: 763
K
Member
I would gander that the high frequency two-way data communication is likely screwing with the electronics in the AFCI itself. I'm guessing they were probably only designed to be used with 60Hz, so here is possibly another application from advances in new technology that AFCI’s were never intended to handle.


I would shoot the circuit breaker manufacturer an email so they can begin to make revisions to the next generation of AFCI and add another $20.00 on to the current price for their efforts. frown


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 240
Joined: March 2005
Top Posters(30 Days)
BigB 2
Popular Topics(Views)
303,295 Are you busy
232,253 Re: Forum
217,014 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5