ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
VFD MotorFeeders
by Yoopersup. 10/17/17 09:50 AM
What do you do?
by gfretwell. 10/17/17 01:08 AM
Good ol' copper pipe in the fuse holder trick
by HotLine1. 10/16/17 07:16 PM
Generator Cable Sizing
by HotLine1. 10/16/17 07:13 PM
Another generator question
by HotLine1. 10/16/17 07:02 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,343 Are you busy
177,294 Re: Forum
168,924 Need opinion
Who's Online Now
0 registered members (), 68 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#203327 - 09/21/11 09:18 PM generator transfer switch  
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
I am planning on installing a manual transfer switch (200A) for a standby residential generator. The transfer switch will be immediately after the main 200Amp disconnect. My question is do i need to have a fused or non-fused transfer switch. Please provide NEC reference so i will learn and know for future.

Thanks for the replies


Be kind to your neighbor, he knows where you live


2017 / 2014 NEC & Related Books and Study Guides

#203329 - 09/22/11 10:58 AM Re: generator transfer switch [Re: Niko]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,327
Alaska
It will have alot to do with which code revision you are under and local code. I'm out of the office and way from me code books as long as you wire the switch as a 200 and switch all the way through you generator panel then I don't see a need for additional OCPD's. It's protected.

A little side note with my inspector cap on, its my humble opinion even though it sounds like you are just doing an add on, it has to meet current code. I do belive in the 2008 cycle requires an automatic switch, not manual


"Live Awesome!" - Kevin Carosa

#203330 - 09/22/11 11:24 AM Re: generator transfer switch [Re: Niko]  
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
We are under the 2008 NEC and it seems Manual switch is allowed. The main service is 200Amps but the portable generator is rated at 50Amps. I am installing 200Amp switch for future capability.


Be kind to your neighbor, he knows where you live


#203334 - 09/22/11 05:46 PM Re: generator transfer switch [Re: Niko]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
If itís a 200A transfer switch on the load side of the 200A service disconnecting means, I donít see why it would need to be fused, especially if its service rated and sized for the full load.
I donít see anything the NEC that would require it either and I have never been required to install a fused transfer switch on a residence before. The generators Iíve installed all had their own built in OCP, which was rated lower than the maximum rating of the transfer switch.


#203335 - 09/22/11 05:48 PM Re: generator transfer switch [Re: Niko]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Niko:

Ditto to what Kjay said above. OCP before xfr switch & full rated & service rated...no issues.



John

#203338 - 09/22/11 07:25 PM Re: generator transfer switch [Re: Niko]  
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
I appreciate your replies.

Learning never exhausts the mind.


Be kind to your neighbor, he knows where you live



Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 15 (0.003s) Memory: 0.7777 MB (Peak: 0.9260 MB) Zlib enabled. Server Time: 2017-10-17 20:45:50 UTC