phase converter problems? #203186 09/13/11 07:32 PM
Joined: Oct 2001
Posts: 172
W
watthead Offline OP
Member
I need an expert or someone with a working knowledge of phase generators. I have phase convertor that runs a small piece of equipment with 3 three phase motors. The problem is a 5hp fan motor is going out on overload. I believe the problem is in the convertor but I am not sure. The single phase 240v supply to the convertor is good. The no load voltages at the convertor are A=122v B=122V C=196v AB=244v BC=210v AC=206v. The currents at the 5hp fan motor are A=2.9 B=20.2 C=13.1 under this load the voltages are AB=240 BC=196 AC=206 Anyone have any ideas or suggestions to determine the actual problem. They would be more than welcomed

Work Gear for Electricians and the Trades
Re: phase converter problems? [Re: watthead] #203188 09/13/11 10:46 PM
Joined: Nov 2005
Posts: 806
J
JoeTestingEngr Offline
Member
You should probably supply info on the type of converter that you are using.
Joe

Re: phase converter problems? [Re: watthead] #203189 09/13/11 11:38 PM
Joined: Oct 2001
Posts: 172
W
watthead Offline OP
Member
it is a rotary converter that has been in service for a couple of years.

Re: phase converter problems? [Re: watthead] #203190 09/14/11 12:21 AM
Joined: Jul 2004
Posts: 783
L
LarryC Offline
Member
When you open up the converter, it has a bunch of canned power capacitors, correct? If so, my GUESS is that you have some bad capacitors. Look for the ones that are swelled or really hot.

Did you have some recent power outages or local lightning strikes? Those caps are AC rated electrolytics. Make sure if they need to be replaced, that you pay attention to the voltage ratings. If I remember right, they were typically rated for 600 VAC.

Re: phase converter problems? [Re: watthead] #203191 09/14/11 12:53 AM
Joined: Oct 2001
Posts: 172
W
watthead Offline OP
Member
Yes there are capacitors inside the starter enclosure. I will check those , thanks.

Re: phase converter problems? [Re: watthead] #203212 09/14/11 06:32 PM
Joined: Oct 2001
Posts: 172
W
watthead Offline OP
Member
Thanks Larry, it was the capacitors. Both run capacitors were bad and when replaced the B phase current fell drastically.

Re: phase converter problems? [Re: watthead] #203218 09/14/11 10:50 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
Not withstanding their higher price -- you're better off with Run Caps...

They're made to MUCH higher standards.


Tesla

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
dsk 7
djk 3
andey 3
Popular Topics(Views)
263,647 Are you busy
198,705 Re: Forum
187,603 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3