Is a conduit up out of the floor supporting a box with a receptacle an acceptable installation?
(for a piece of kitchen equipment out in the middle of the floor (not near a wall))

Joined: Jan 2005
Posts: 5,316
Cat Servant
Member
Sure, you can do it. BUT ....

Be aware that the thing will have the living daylights beat out of it as the tables get shifted about and the floor gets hosed off. Plan accordingly.

Which means ... 3/4 rigid stub-ups, a second support to keep the box from twisting, compression connectors to allow future box replacement, and cast-iron FS-type boxes (not the wimpy Bell boxes). AND have the GFCI somewhere else.

Joined: Jun 2004
Posts: 1,273
T
Member
Normally pendent drops are used.

The Health Inspector will normally be your objecting party.


Tesla
Joined: Apr 2002
Posts: 7,282
Likes: 3
Member
cgw:

I agree with Reno & Tesla. I would also add...check with your local AHJ first.

Last edited by HotLine1; 07/20/11 08:44 PM.

John
Joined: Jul 2004
Posts: 9,668
Likes: 6
G
Member
In the fast food business I saw a mix of the FS boxes Reno described on 3/4" RMC stub ups and pendants.
They really try to put in a stem wall with regular receptacles on them and FRP sheathing or tile for the wash down. I imagine with the GFCI requirement the pendants are even more attractive.


Greg Fretwell
Joined: May 2005
Posts: 984
G
Member
If you're using GRC and cast boxes, you'll have to use Erickson couplings if you want to make any future box replacement easier. Also, the permanent location of the box will interfere with any future rearrangement of the Kitchen.
I vote for using drops like you see at all of the McDonalds.


Ghost307

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Top Posters(30 Days)
dsk 7
Popular Topics(Views)
284,761 Are you busy
217,372 Re: Forum
203,712 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5