floor receptacle in commercial kitchen #202141 07/20/11 02:15 PM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
Is a conduit up out of the floor supporting a box with a receptacle an acceptable installation?
(for a piece of kitchen equipment out in the middle of the floor (not near a wall))

Work Gear for Electricians and the Trades
Re: floor receptacle in commercial kitchen [Re: cgw] #202146 07/20/11 04:08 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Sure, you can do it. BUT ....

Be aware that the thing will have the living daylights beat out of it as the tables get shifted about and the floor gets hosed off. Plan accordingly.

Which means ... 3/4 rigid stub-ups, a second support to keep the box from twisting, compression connectors to allow future box replacement, and cast-iron FS-type boxes (not the wimpy Bell boxes). AND have the GFCI somewhere else.

Re: floor receptacle in commercial kitchen [Re: cgw] #202152 07/20/11 06:43 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
Normally pendent drops are used.

The Health Inspector will normally be your objecting party.


Tesla
Re: floor receptacle in commercial kitchen [Re: cgw] #202153 07/20/11 07:05 PM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
cgw:

I agree with Reno & Tesla. I would also add...check with your local AHJ first.

Last edited by HotLine1; 07/20/11 07:44 PM.

John
Re: floor receptacle in commercial kitchen [Re: cgw] #202157 07/20/11 08:55 PM
Joined: Jul 2004
Posts: 9,568
G
gfretwell Offline
Member
In the fast food business I saw a mix of the FS boxes Reno described on 3/4" RMC stub ups and pendants.
They really try to put in a stem wall with regular receptacles on them and FRP sheathing or tile for the wash down. I imagine with the GFCI requirement the pendants are even more attractive.


Greg Fretwell
Re: floor receptacle in commercial kitchen [Re: cgw] #202166 07/20/11 10:30 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
If you're using GRC and cast boxes, you'll have to use Erickson couplings if you want to make any future box replacement easier. Also, the permanent location of the box will interfere with any future rearrangement of the Kitchen.
I vote for using drops like you see at all of the McDonalds.


Ghost307

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,348 Are you busy
209,214 Re: Forum
196,517 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3