ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Inspections and Testing
by Texas_Ranger. 04/24/18 07:09 AM
FEMA height and electrical equiment.,
by HotLine1. 04/20/18 08:49 AM
This anti-theist is priceless!!!
by LongRunner. 04/19/18 04:02 PM
Recall notice: Square D Services Switches
by gfretwell. 04/18/18 01:24 PM
Big Square D service switch Recall
by sparkyinak. 04/18/18 12:30 AM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
1 registered members (brsele), 12 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
floor receptacle in commercial kitchen #202141
07/20/11 03:15 PM
07/20/11 03:15 PM
C
cgw  Offline OP
Member
Joined: Jul 2004
Posts: 133
Rochester NY
Is a conduit up out of the floor supporting a box with a receptacle an acceptable installation?
(for a piece of kitchen equipment out in the middle of the floor (not near a wall))

Work Gear for Electricians and the Trades
Re: floor receptacle in commercial kitchen [Re: cgw] #202146
07/20/11 05:08 PM
07/20/11 05:08 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Sure, you can do it. BUT ....

Be aware that the thing will have the living daylights beat out of it as the tables get shifted about and the floor gets hosed off. Plan accordingly.

Which means ... 3/4 rigid stub-ups, a second support to keep the box from twisting, compression connectors to allow future box replacement, and cast-iron FS-type boxes (not the wimpy Bell boxes). AND have the GFCI somewhere else.

Re: floor receptacle in commercial kitchen [Re: cgw] #202152
07/20/11 07:43 PM
07/20/11 07:43 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Normally pendent drops are used.

The Health Inspector will normally be your objecting party.


Tesla
Re: floor receptacle in commercial kitchen [Re: cgw] #202153
07/20/11 08:05 PM
07/20/11 08:05 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,949
Brick, NJ USA
cgw:

I agree with Reno & Tesla. I would also add...check with your local AHJ first.

Last edited by HotLine1; 07/20/11 08:44 PM.

John
Re: floor receptacle in commercial kitchen [Re: cgw] #202157
07/20/11 09:55 PM
07/20/11 09:55 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,199
Estero,Fl,usa
In the fast food business I saw a mix of the FS boxes Reno described on 3/4" RMC stub ups and pendants.
They really try to put in a stem wall with regular receptacles on them and FRP sheathing or tile for the wash down. I imagine with the GFCI requirement the pendants are even more attractive.


Greg Fretwell
Re: floor receptacle in commercial kitchen [Re: cgw] #202166
07/20/11 11:30 PM
07/20/11 11:30 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 935
Chicago Illinois USA
If you're using GRC and cast boxes, you'll have to use Erickson couplings if you want to make any future box replacement easier. Also, the permanent location of the box will interfere with any future rearrangement of the Kitchen.
I vote for using drops like you see at all of the McDonalds.


Ghost307

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
245,910 Are you busy
182,968 Re: Forum
172,779 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.030s Queries: 15 (0.004s) Memory: 0.9770 MB (Peak: 1.1263 MB) Zlib enabled. Server Time: 2018-04-24 17:59:57 UTC