Installing Electric Heaters in dwelling (Art.424) #201581
06/10/11 07:10 PM
06/10/11 07:10 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
couple Questions:
424.3 Branch circuits Allows 15/20/25/30.
Electric heat Thermostates come as high as 22 amps as far as I see. So over 20 Amps Contactor required.

Thermostate rated 125 & of load (unit Switch as disconnect 424.20) =
Off position / two poles Located per 424.19.Within sight of heater OR breaker lock on branch circuit breaker rated 125% of Load.

Another words if a Heater is Not within sight of the ther.
there must be a Fixed breaker lock on breaker feeding that circuit.

Ther. Must be 2 pole , rated 125% of load, Off position,
not over 20 amps without a contactor, within sight of heater unless breaker lock on circuit breaker.

Whatca Think Guys??

2017 / 2014 NEC & Related Books and Study Guides
Re: Installing Electric Heaters in dwelling (Art.424) [Re: Yoopersup] #201588
06/10/11 11:44 PM
06/10/11 11:44 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,972
Brick, NJ USA
Yoop:

Most (if not all) BB Elec heta I installed was with LV t'stats and contactors w/12/24 volt coils. That method of control for simplicity and installation ease.

The LV t'stat & contactor always worked out to a less costly install for me, and it allowed larger loads to be controlled by a t'stst.

The answer to your question IMHO is 'Yes'...2 pole, off position, 125% rated, within site....or a breaker lockout.



John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
twh 5
Popular Topics(Views)
247,578 Are you busy
184,909 Re: Forum
174,136 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 15 (0.004s) Memory: 0.9439 MB (Peak: 1.0613 MB) Zlib enabled. Server Time: 2018-06-18 20:58:34 UTC