Are US breakers typically thermal-magnetic? #201258 05/23/11 06:05 AM
Joined: Dec 2001
Posts: 2,491
T
Texas_Ranger Offline OP
Member
Over on the German board the question arose, whether US breakers for residential use are typically equipped with both a thermal and an electromagnetic tripping device or only either of them.

In all countries that use DIN rail equipment they seem to alyways have both, is that true for the US too?

Work Gear for Electricians and the Trades
Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger] #201259 05/23/11 07:47 AM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
The statement is true for breakers found in the typical panel.

There are some breakers used in motor control centers that lack the magnetic function.

Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger] #201265 05/23/11 01:37 PM
Joined: Dec 2001
Posts: 2,491
T
Texas_Ranger Offline OP
Member
Thanks a lot! For motor controls, omitting the magnetic trip makes sense since the short-circuit protection can be achieved by a much larger fuse upstream.

Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger] #201325 05/28/11 04:32 AM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
Originally Posted by Texas_Ranger
Over on the German board the question arose, whether US breakers for residential use are typically equipped with both a thermal and an electromagnetic tripping device or only either of them.

In all countries that use DIN rail equipment they seem to alyways have both, is that true for the US too?


It the same in France we have both thermal and magatic breakers as well but few of the breakers may not have magatic at all I know I have ran into hydrallic breaker { kinda oddball item }

Merci.
Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger] #201326 05/28/11 06:36 AM
Joined: Dec 2001
Posts: 2,491
T
Texas_Ranger Offline OP
Member
The hydraulic surely wasn't the typical 10, 16 or 20A household type, was it?

I'm interested in what you'd typically find in an apartment or single family home, as that was what the original discussion was concerned with.

Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger] #201338 05/28/11 09:17 PM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
Reno,


Are we talking about FPE breakers? smile

Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger] #201342 05/28/11 09:27 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
This is a SqD QO GFCI I cut open to see what was inside.I was really interested in the GFCI part but you can see the breaker part too. It looks like it is thermal only.

[Linked Image from gfretwell.com]


Greg Fretwell
Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger] #201343 05/28/11 09:29 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Harold, I cannot even attempt to explain the engineering miracle represented by FPE and their breakers.

Imagine ... a breaker that works so well in Canada that it's sold by Schneider Electric (alongside their competing Square D line), yet somehow fails to perform 'south of the border.'

Perhaps us hapless Yanks are simply not sophisticated enough to use these advanced devices laugh

Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger] #201348 05/28/11 09:53 PM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
Reno,

I believe the FPE breakers actually worked well with a thermal overload. It was those quick short circuit faults that they didn't seem to see.

Re: Are US breakers typically thermal-magnetic? [Re: renosteinke] #201410 05/31/11 11:48 AM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Originally Posted by renosteinke
There are some breakers used in motor control centers that lack the magnetic function.


Nope.

The "typical" breaker in a motor control center is Magnetic only. The thermal function is handled by the motor starter's overload relay.

Page 1 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,437 Are you busy
209,330 Re: Forum
196,614 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3