#201118 05/12/11 08:19 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Can I use a panel with a GFCI main as GFCI protection for the requirements found in 680 covering the pump motors, underwater lights, pool cover and the lights and receptacles around the pool area?


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,868
Likes: 25
G
Member
It might end up being a horrible design choice but I can't think of a reason why it is not code compliant.

As a friend I would point out finding a random nuisance tripping problem would be a nightmare.


Greg Fretwell
Joined: Apr 2002
Posts: 7,371
Likes: 7
Member
George:
You did not mention if the 'GFI Main' is 'Class A'. That's the only possibility I can muster at the moment.

As Greg alluded...I sure would not look forward to a troubleshoot job with that arrangement.

Are you heading in any direction with this?



John
Joined: Jul 2004
Posts: 9,868
Likes: 25
G
Member
I assumed they were going to use the typical "spa" type 50-60A GFCI and sub off of that to avoid buying several 1 & 2 pole GFCIs for pumps, cover, lights etc. (maybe I am off base)

If everything was 120v I doubt it makes any sense at all since those GFCIs are cheap ... unless that was just what he had on the truck. wink


Greg Fretwell
Joined: Jan 2004
Posts: 1,507
G
Member
Okay, you guys know my MO, I was involved with a situation where the contractor wanted to use a Class A GFCI Main in a panel as permitted in 215.19. But when you read into the references it refers to 210.8 and 590.6(A). When you have equipment in 680 requiring GFCI protection such as the lighting, the pumps, the cover the receptacles, the cost effective way could be to install a single Main. The problem becomes that in 680.23(A)(3) it specifically says that the GFCI protection must be in the branch circuit feeding the luminaires. Putting it in the feeder is a violation. This has been confirmed by a member of code panel 17. Yah, I was trying to trick you guys again.


George Little
Joined: Apr 2002
Posts: 7,371
Likes: 7
Member
George:
Keep up the good work!!!!


John
Joined: Jul 2004
Posts: 9,868
Likes: 25
G
Member
He got me wink


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
Popular Topics(Views)
311,074 Are you busy
237,472 Re: Forum
221,260 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5