ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Danish type K Sockets
by winston_1 - 10/25/21 07:30 PM
Flexible Conduit?
by gfretwell - 10/24/21 01:59 AM
May I backfeed 3 phase transformer?
by dsk - 10/22/21 04:37 AM
Wire sizing
by gfretwell - 10/21/21 10:12 PM
GFCI's pops in large numbers
by dsk - 10/21/21 02:03 AM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 16 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#201118 05/12/11 08:19 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Can I use a panel with a GFCI main as GFCI protection for the requirements found in 680 covering the pump motors, underwater lights, pool cover and the lights and receptacles around the pool area?


George Little
2017 / 2014 NEC & Related Books and Study Guides
Joined: Jul 2004
Posts: 9,669
Likes: 6
G
Member
It might end up being a horrible design choice but I can't think of a reason why it is not code compliant.

As a friend I would point out finding a random nuisance tripping problem would be a nightmare.


Greg Fretwell
Joined: Apr 2002
Posts: 7,283
Likes: 3
Member
George:
You did not mention if the 'GFI Main' is 'Class A'. That's the only possibility I can muster at the moment.

As Greg alluded...I sure would not look forward to a troubleshoot job with that arrangement.

Are you heading in any direction with this?



John
Joined: Jul 2004
Posts: 9,669
Likes: 6
G
Member
I assumed they were going to use the typical "spa" type 50-60A GFCI and sub off of that to avoid buying several 1 & 2 pole GFCIs for pumps, cover, lights etc. (maybe I am off base)

If everything was 120v I doubt it makes any sense at all since those GFCIs are cheap ... unless that was just what he had on the truck. wink


Greg Fretwell
Joined: Jan 2004
Posts: 1,507
G
Member
Okay, you guys know my MO, I was involved with a situation where the contractor wanted to use a Class A GFCI Main in a panel as permitted in 215.19. But when you read into the references it refers to 210.8 and 590.6(A). When you have equipment in 680 requiring GFCI protection such as the lighting, the pumps, the cover the receptacles, the cost effective way could be to install a single Main. The problem becomes that in 680.23(A)(3) it specifically says that the GFCI protection must be in the branch circuit feeding the luminaires. Putting it in the feeder is a violation. This has been confirmed by a member of code panel 17. Yah, I was trying to trick you guys again.


George Little
Joined: Apr 2002
Posts: 7,283
Likes: 3
Member
George:
Keep up the good work!!!!


John
Joined: Jul 2004
Posts: 9,669
Likes: 6
G
Member
He got me wink


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Top Posters(30 Days)
dsk 7
Popular Topics(Views)
284,883 Are you busy
217,430 Re: Forum
203,743 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5