Splice in service disconnect #200399 03/30/11 07:33 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
A 400amp main disconnect will need to be added outside a Building. Existing is a 400 amp main circuit breaker panel in the utility room. The Arc flash rating turned out to be a Cat. 4 for the Panel.(you have to wear a space suit) so by installing a Disconnect between the Panel and the transformer, the engineer says it will go to a category 2. This is fed from a pad mount transformer with the metering mounted on the outside. Can the feeders from the transformer be spliced in the disconnect if not long enough, to go to the line side of the switch? Or will we have to install a 2'x2' junction box. Existing, is the 4" LB going to the back of the Main Panel.
Sorry about the long story - Thanks, SJT

Work Gear for Electricians and the Trades
Re: Splice in service disconnect [Re: SJT] #200401 03/30/11 09:29 PM
Joined: Apr 2002
Posts: 7,218
HotLine1 Offline
Member
IMHO, run this past the local AHJ first. Also you may have to run it by the local POCO. 'Line' side may be POCO jurisdiction. Using barrel crimps should be acceptable.



John
Re: Splice in service disconnect [Re: SJT] #200432 04/01/11 09:06 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
I'm sorry I only have my 2008 NEC with me, ( we are still on that code) but would 230.33 be of use in this case?

Re: Splice in service disconnect [Re: SJT] #200437 04/01/11 10:03 AM
Joined: Apr 2002
Posts: 7,218
HotLine1 Offline
Member
harold:
230.33 refers you to 110.14 regarding splicing methodology, and refers to 300.xx articles which I understand are not applicable in the OP.

I mentioned the local POCO, and AHJ for a few reasons. Here (PS) crimp splices are acceptable on a case by case basis, as they are by me, and most other AHJs. Extending an existing lateral feeder to terminate at the line side of a disconnect switch, in lieu of replacement of that feeder can be acceptable. Crimp splice; feeder in acceptable condition, and sufficient 'space' within the disco.



John
Re: Splice in service disconnect [Re: SJT] #200464 04/02/11 12:19 PM
Joined: Jul 2004
Posts: 9,542
G
gfretwell Offline
Member
I only had the "splice in the disco" come up once and I agreed to the irreversible crimp splice, simply because any alternative was very burdensome on the installer and I did not see any particular hazard. We were literally talking about a foot of wire.


Greg Fretwell
Re: Splice in service disconnect [Re: SJT] #200468 04/02/11 12:33 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
Thanks for the inputs,
I think I'll go with the barrel crimps, if the wires are not long enough.
SJT


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,998 Are you busy
205,882 Re: Forum
193,943 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3