#200191 03/24/11 12:46 PM
Joined: Oct 2002
Posts: 830
S
Member
Tell me if I'm right:
If I run 12/3 UF cable to a detached garage to feed lights and receptacles I would not have to drive a ground rod at the detached building??? I know to put a double pole breaker on the multi/wire circuit. Also will I have to provide another means of disconnect at the garage for the circuits??
I'm not planning on doing it like this, but just in case the customer wants to go the cheapest route, I want to make sure. Thanks for the input

Horizontal Ad
Joined: Jul 2004
Posts: 10,026
Likes: 37
G
Member
Just don't call it a feeder, it is a "single branch circuit" and put the breaker on the line end, in the house. Then you get the exceptions.
You still need a disconnect but that can be a 2 pole snap switch or two single poles marked "disconnect". The switches have to be rated at the load and 15a or greater.
Personally I would use a 2 pole 30a to make everyone happy.
(Ref 225.30-225.39)


Greg Fretwell
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
2008 NEC 250.32(A) exception:

Exception: A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non–current-carrying metal parts of equipment.



John
Joined: Oct 2002
Posts: 830
S
Member
Thanks for the replies. That's what I was thinking but just didn't have the code reference available. Greg, would it not still be considered a "branch circuit" even if I did come out of the outside panel, as long as the outside panel has a "main breaker" in it?? Thanks again.

Joined: Jul 2004
Posts: 10,026
Likes: 37
G
Member
As long as it is on the load side of the last over current device it is a branch circuit.


Greg Fretwell

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
richard
richard
L.I. New York
Posts: 99
Joined: August 2003
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
553,529 Are you busy
428,145 Re: Forum
398,284 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5