12/3 feeder to garage #200191 03/24/11 12:46 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
Tell me if I'm right:
If I run 12/3 UF cable to a detached garage to feed lights and receptacles I would not have to drive a ground rod at the detached building??? I know to put a double pole breaker on the multi/wire circuit. Also will I have to provide another means of disconnect at the garage for the circuits??
I'm not planning on doing it like this, but just in case the customer wants to go the cheapest route, I want to make sure. Thanks for the input

2017 / 2014 NEC & Related Books and Study Guides
Re: 12/3 feeder to garage [Re: sparkync] #200196 03/24/11 02:40 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
Just don't call it a feeder, it is a "single branch circuit" and put the breaker on the line end, in the house. Then you get the exceptions.
You still need a disconnect but that can be a 2 pole snap switch or two single poles marked "disconnect". The switches have to be rated at the load and 15a or greater.
Personally I would use a 2 pole 30a to make everyone happy.
(Ref 225.30-225.39)


Greg Fretwell
Re: 12/3 feeder to garage [Re: sparkync] #200197 03/24/11 02:41 PM
Joined: Apr 2002
Posts: 7,233
HotLine1 Offline
Member
2008 NEC 250.32(A) exception:

Exception: A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non–current-carrying metal parts of equipment.



John
Re: 12/3 feeder to garage [Re: HotLine1] #200201 03/24/11 05:41 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
Thanks for the replies. That's what I was thinking but just didn't have the code reference available. Greg, would it not still be considered a "branch circuit" even if I did come out of the outside panel, as long as the outside panel has a "main breaker" in it?? Thanks again.

Re: 12/3 feeder to garage [Re: sparkync] #200203 03/24/11 09:08 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
As long as it is on the load side of the last over current device it is a branch circuit.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,432 Are you busy
209,320 Re: Forum
196,607 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3