ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Admin 2
Recent Posts
Casino Wiring methods
by HotLine1. 12/09/17 10:44 AM
Ground wire Size to water Line.
by HotLine1. 12/05/17 12:11 PM
Flexible conduit to an outside Spa
by gfretwell. 12/05/17 12:28 AM
2017 NEC Changes
by luckyshadow. 12/04/17 06:08 PM
Dimmable LED 2x4 lay in fixtures
by Vulsion. 11/30/17 06:37 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
242,992 Are you busy
179,386 Re: Forum
170,355 Need opinion
Who's Online Now
0 registered members (), 9 guests, and 14 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#199254 - 02/17/11 09:48 PM Thought experiment with xfmrs and lamps  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Thought experiment:

Three single phase pole mount transformers 4160/240 CT

High voltage is 4160 Wye, Low votage 120/240 CT delta.

High voltage and low voltage share common neutral/earth.

Car accident isolates neutral from rest of power distribution network. The three 4160 lines are still intact, the earth connection via building bonds still intact.

Q1) If transformers are equally loaded, no shift on high voltage side. Correct?

Q2) Assuming stable transformer loading, no shift on low voltage side too?

Q3) What happens when most of 3 phase loads dissapear, leaving a significant single phase load?

Thanks

LarryC


Work Gear for Electricians and the Trades

#199257 - 02/17/11 11:01 PM Re: Thought experiment with xfmrs and lamps [Re: LarryC]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,140
Estero,Fl,usa
The line to neutral loads will balance, just like in a regular120/240. If one side is more heavily loaded, the magic smoke will be coming out of the other side. Motors on both sides are in danger.


Greg Fretwell

#199263 - 02/18/11 01:32 PM Re: Thought experiment with xfmrs and lamps [Re: gfretwell]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Would the HV "neutral" shift with the unbalance and difference between this "neutral" and the rest of the power company "neutrals" in the area, result in current thru all available paths like the plumbing and the earth itself?


#199264 - 02/18/11 02:41 PM Re: Thought experiment with xfmrs and lamps [Re: LarryC]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,140
Estero,Fl,usa
If you are talking about losing the neutral on the line side of the pole pigs, it would really depend on where you lived. Some places have a better "ground" than others. If this was metal water piping, all the way back to the pumping station, you might not even notice the neutral was gone. If you are in Florida with plastic piping and sand around the electrodes, you are still going to balance the loads and the neutral will track that ratio. This is where you could be saved by diversity. The more customers you have on the load side of the break, the better chance you have that the loads will balance. It is still going to be pretty unstable.


Greg Fretwell


Member Spotlight
Admin
Admin
NY, USA
Posts: 3,460
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.002s) Memory: 0.7619 MB (Peak: 0.8926 MB) Zlib enabled. Server Time: 2017-12-11 09:06:44 UTC