Readily available (Ha Ha) AFCI Receptacle! #199054 02/11/11 10:51 PM
Joined: Jan 2011
Posts: 64
P
PAteenlectrician Offline OP
Member
When will the AFCI receptacles be available?

2017 / 2014 NEC & Related Books and Study Guides
Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician] #199088 02/13/11 01:04 AM
Joined: Jan 2011
Posts: 64
P
PAteenlectrician Offline OP
Member
Your utter silence tells me you don't know.

Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician] #199093 02/13/11 11:52 AM
Joined: Apr 2002
Posts: 7,235
HotLine1 Offline
Member
PAteen:

There are quite a few threads on the elusive AFCI device in the forum.

The 'latest sighting' was within the 2011 NEC Changes book(s), again showing the 'prototype' device from P&S Legrand. My person info on this is from a P&S rep; "not available!"

End of story!


John
Re: Readily available (Ha Ha) AFCI Receptacle! [Re: HotLine1] #199094 02/13/11 01:40 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
AFAIK, they are still not currently available and since they arenít required for replacement purposes until 2014, my guess is that manufactures are probably not in any rush to produce them.

Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician] #199114 02/13/11 10:03 PM
Joined: Jan 2011
Posts: 64
P
PAteenlectrician Offline OP
Member
I wish they are available now, for even more safety in my extension cords. My house is wired with romex, so I cannot use them there.

Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician] #199115 02/13/11 10:49 PM
Joined: Sep 2006
Posts: 155
C
crselectric Offline
Member
why would you not be able to use them on romex?? confused

Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician] #199116 02/13/11 11:06 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
210.12 Exception No. 1: Where RMC, IMC, EMT or steel armored cable, Type AC, meeting the requirements of 250.118 using metal outlet and junction boxes is installed for the portion of the branch circuit between the branch-circuit overcurrent device and the first outlet, it shall be permitted to install a combination AFCI at the first outlet to provide protection for the remaining portion of the branch circuit.


Greg Fretwell
Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician] #199123 02/14/11 10:50 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
I was told by one of the manufacturers that they realize that they'd sell a ton of them in Chicago, where metallic conduit is required for just about everything; but that they doubt that starting up a product with only 1 local market makes any economic sense.

And if Chicago ever drops that requirement...there would be zero buyers anymore.

Something tells me that these will not be available...at least not from any of the usual reputable manufacturers.


Ghost307
Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician] #199126 02/14/11 12:17 PM
Joined: Jan 2011
Posts: 64
P
PAteenlectrician Offline OP
Member
I can see it being used. Not too often, though.

Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician] #199127 02/14/11 12:32 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
HUH?

As I see it , the real advantage is for use in replacing existing receptacles in existing construction. I believe it is the intent to require such a receptacle to be used in repairs to non-AFCI-protected circuits after the next code cycle.

(Guess that means they'll want them to be tamper-resistant as well. Can this possible become more of a cluster-flock than it already is?)

Likewise, the 'first receptacle' business allows us to add AFCI protection to an old home that has a fuse box or obsolete panel. Since the expressed purpose of these gizmos is to prevent fires from frayed wiring, it seems logical that it's the OLD homes that need them the most.

There's a certain amount of BS in the distribution chain. When AFCI's were first introduced, Leviton was swearing, and the UL plant inspector verified, that they had pallets of these things in the warehouse. Yet, Graybar was telling me that they were 'not available.' I ran into a similar issue with CED. Only several months after the AFCI requirement was locally adopted did the things suddenly become 'available.'

It's not the only item where the supply house, and the manufacturer, had differing views. Heck, I've often encountered different views between the manufacturers and their own advertising. Sometimes I'm amazed that anything ever reaches the intended user!

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,704 Are you busy
209,627 Re: Forum
196,966 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3