N
Member
This requirement looks like if a fuel dispenser is less than 20 feet from the door the entire store will have to be wired as Class I, Division 2.
It says, Sales, Storage, Rest Rooms including structures (such as the attendant’s kiosk) on or adjacent to dispensers....Entire volume, if there is ANY opening to room within the extent of a Division 2 or Zone 2 location the entire volume shall be Class I, Division 2.
I bet half the gas station in my local community have doors that open into a Class I, Division 2 location because the doors are within 20 feet of the dispensers.
Any comments?

2017 / 2014 NEC & Related Books and Study Guides
Joined: Jul 2004
Posts: 9,673
Likes: 7
G
Member
Usually the fueling island is more than 20' away at the ones I see but the kerosene pump right next to the building could be troublesome.


Greg Fretwell
Joined: Feb 2011
Posts: 15
N
Member
I checked a major gas station owned by the Koch Brothers of Flint Hills and the dispensers were 18 feet from the door. The rule says ANY opening and that would mean a door from the way I read it. If the door stayed closed it might not count, but whenever it opens it is an opening. This rule is going to cause problems!

Joined: Jul 2004
Posts: 9,673
Likes: 7
G
Member
I wonder what the fire marshal says about it?
It might be some kind of godfathered thing. The "shop and robs" around here usually have the islands pretty far from the building because they are in line with the window. (easier to see a "drive away")
That means they have the driveway and usually some parking in between them.


Greg Fretwell
Joined: Feb 2011
Posts: 15
N
Member
The NEC generally is not retroactive but applies to new construction only. So existing structures probably will be grandfathered. However, this new change does present some liability issues if there is a fire or explosion at existing facilities. It looks like the Code Making Panel slipped this one in without fully discussing the change. Supposedly this new Table was adopted from NFPA 30A and was derived from Tentative Interim Amendment (TIA) 08-01 that was issued August 6, 2009 to NFPA 30A according to the IAEI Analysis of Changes for the 2011 NEC.

Joined: Jul 2004
Posts: 9,673
Likes: 7
G
Member
The "leaking tank" issue closed most of the old gas stations around here. They pretty much made it "prove your old tank isn't leaking" and it was cheaper to just close the station. They were either torn down or they are some other kind of store now. These days virtually every station in town is a new mini mart with the fueling islands out in the middle of the lot. Out of town, some do still have a kerosene pump and that is closer to the building. That one could be troubling.


Greg Fretwell
Joined: Feb 2011
Posts: 15
N
Member
We had the same problem with the leaking tanks and many independents went out of business. Some new stations built in the last 25 years still have the problem of less than 20 feet from the door to the gasoline dispensers. Diesel should not be a problem since diesel is not a flammable liquid because it has a flash point above 100 degrees F and does not fall under Table 514.3(B)(1). However, JP4 is a flammable liquid as is Jet B jet fuel.
This should be picked up on plan reviews for jurisdictions that have plan reviews.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Top Posters(30 Days)
NORCAL 1
Popular Topics(Views)
286,628 Are you busy
219,101 Re: Forum
205,193 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5