Where can I find the code requiring the removal of abandoned cables and conductors unless they are labled "spare" or "for future use"?

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jul 2004
Posts: 10,039
Likes: 37
G
Member
There are rules in cellular raceway system, low voltage, alarm and data center articles but I don't know of anything specific in article 300 wiring.


Greg Fretwell
Joined: Jan 2004
Posts: 1,507
G
Member
Greg I don't know if this is relevant or not but 590.3(D) might apply depending on what the OP is talking about. And if it's one of the cables in Chapter 7 or 8 they need to be removed or tagged per XXX.25

Last edited by George Little; 01/29/11 06:10 PM.

George Little
Joined: Apr 2002
Posts: 203
T
triple Offline OP
Member
Thank you Mr Little. That was the info I was looking for. Using your help and the additional information available in the Handbook, I found a total of ten articles related to this subject.